Hi peeps, go easy on me I don't often post on forums.

I'm working on a school at the moment and several areas have emergency stop systems installed. These are designed to kill the local power circuits with multiple EPO switches.

Whenever I've installed similar systems we've used NO contactors with NC EPO switches wired in series feeding the coils. On this job the circuits that had already been installed when I got there were the reverse, with NC contactors and NO switches wired in parallel.

I can see how both systems would work. The reason I thought you aways did it the way I knew was because it is self monitoring for faults and the default state is with the circuits disconnected. This seems pretty important to me for a safety system.

There were two reasons I was given for their system. One was that multiple contactors can 'chatter' causing unspecified problems. Also that the contactors will burn out.

Can anyone advise me what exactly contactor chatter is and how it might affect the system and/or how long these contactors might last? Or if there has been a discussion elsewhere about these issues point me in the right direction? Or finally if someone knows of a better system altogether?

Many thanks in advance.
 
Putting NC e-stops in series with the coil of a NO contactor is the simplest and safest way to achieve fail safe operation of that circuit. I don't see how you could get chatter, if the supply voltage is ok, and uninterrupted.
 
At the correct voltage a contactor will last for years.

Chatter can be put down to several thing:
Low voltage.
Dirt on the clapper faces.
An obstruction preventing the clappers meeting.
Faulty / damaged shading poles in the clapper face.

As to using NO contacts for an E-Stop circuit, it’s downright dangerous. A dirty contact could prevent the contactor operating. As John said a NC circuit is self checking.
 
How do they re-energise the contactors, if this is by release of the e-stops then the circuit is in breach of the CoP for schools, which is a BS.
There are a whole raft of H&S and BS requirements around central emergency switching systems for schools and colleges in the UK.
 
Many thanks for all the replies, it's much appreciated.
Actually to make matters worse since I brought the issue up they've decided to use the method I described in new areas. Now the school has two methods of achieving the emergency stop system. Hopefully they will see sense and alter it.
Does anyone know any good links to info on codes of practice/standards for schools? I'll try & get it off the main contractor although they probably won't want to show it to me after 'causing trouble'.
 
N/C safety cct is as stupid as self resetting safety cct.

They need sorting out immmediately.

I've dealt with contactor controlled ccts including safety ccts for around 40 years and never seen such a thing.
 
I agree.
Just to clarify about self resetting: in the correct system do you consider local 'key to release' NC emergency switches wired in series feeding NO contactors acceptable?
Cheers.
 
As many others here have stated, i too have never seen N/O emg stops.

this week ive been working on an FG wilson generatiors, in which the external and compound e-stops were wired as NO. This has now been altered by the genny supplier, but i was told that they supply them like that as standard. how many of them must be in service with NO e-stops. also the estops input into the controller, and are not wired independanty. Im not too sure about the legislation, but im sure a safety conroller/plc has to be marked as such.
 
We have used F.G. Wilson generators on a few projects, mostly for MV (13.8KV) units. Can't say that i've ever seen N/O em stops, on any of their submitted proposal drawings. That i would have picked up on, ...and changed!! ...lol!!!
 
I agree.
Just to clarify about self resetting: in the correct system do you consider local 'key to release' NC emergency switches wired in series feeding NO contactors acceptable?
Cheers.

Yes as long as releasing the keyed stop button does not re-energise the circuit.
Else it is self resetting.
Another thing is that it is not allowed to have ANY safety related devices connected to a central switching system.
That is no LEV, no dc braking, no flammable gas controls etc.
 

Reply to Contactor chatter and burn out? in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
685
Hello, Last year my 30 year old Static Pase convertor stopped working, the 3 phase motor is 0.55KW / 0.74HP and drives a small lathe. When I...
Replies
0
Views
189

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top