Contactor Conundrum. | on ElectriciansForums

Discuss Contactor Conundrum. in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 24, 2010
Messages
992
Reaction score
126
Location
South east
Greetings.

I have bought myself a Contactor to wire into the garage lights so they switch on when the electric garage door is raised.

[ElectriciansForums.net] Contactor Conundrum.[ElectriciansForums.net] Contactor Conundrum.

Unfortunately it did not come with any literature and seeing as how this is the first time I have ever wired one I thought I would ask here for a bit of advice.

I am guessing that terminals 1 and 2 are for the feed signal from the door and terminals 3 and 4 are for the load which is the supply to the lights.

Is this correct?

The garage door has a small light that illuminates when the door is opened and I was thinking of wiring the feed to the Contactor in parallel with the light.

The supply to the garage lights (load) would go from a 6 Amp MCB, through the Contactor then to the lights and then back to the neutral of the board so the Contactor will be wired in parallel with the garage door light as a feed and in series with the garage lights which are the load.

Can anyone help me with this one?

Thanks very much.
 
A1 and A2 is the coil when you apply 230v to the coil it will close the contactor, check your garage door light is the same voltage as the coil on the contactor, then bring your mcb feed into terminal 1 and switch out of terminal 2, is the light you want to bring on existing and controlled by a switch or is it an independant light running of the contactor only.
 
Last edited:
The issue I forsee is that the lamp in the door motor unit may be a different voltage to the coil contacts in the contactor.

Also, terminating additional cableing to the lamp terminals may be a right PITA.
 
That's great thanks.

I didn't realise A1 and A2 had terminals behind the screws, I was being a bit thick, I couldn't see the terminals at first glance.

The supply/feed to the garage lights will feed two switches.

Each switch will feed one bank of lights, each bank of lights consists of 2 six foot fluoro's so in total there will be four six foot fluoro's supplied by two switches.
Each pair can be switched independently.

So this Contactor is double pole with line load going through 1 and 2 and load neutral going through 3 and 4.
Is this correct?

The lamp in the garage door is definitely 230 Volts I checked.

Also the garage door light/ control signal has a timer built in and so this timer will be handy for turning the garage lights off automatically after about two minutes.

I am not sure what a limit switch is, I shall have to do some reading.
 
Last edited:
Does the indication lamp remain on when the door is open or just when the winding motor operates? If it’s on all the time the door is open your OK, otherwise you’ve got problems.
 
It's a small lamp, low wattage 230V light bulb at the top of the control unit.

When the garage door is switched to open the lamp illuminates and stays illuminated for about two minutes after the garage door has finished opening then switches off.

The same is also true when the garage door shuts. The lamp illuminates when the motor kicks in and the lamp stays illuminated for two minutes after the door has shut.

If I can get the control feed wired OK I will take the supply from a 6 amp MCB, through the Contactor, through the switch and thence to the lights and keep my fingers crossed.
 
Last edited:
You could wire coil as suggested and have a feed from light switch feeding 1 and looping to 3, then 2 is switch to one bank of lights and 4 is switch to other bank of lights, you dont need to run neutral through contactor, this way all lighting will work via contactor.
 
Last edited:
Some garage door unit lamps are supplied via a solid state device ie diac or triac. I would check the circuit first and if the lamp isn't supplied via a relay then use a separate limit switch to operate the contactor as previously suggested.

Also sometimes the garage door unit flashes the lamp several times before the door opens or closes by means of a warning. This would play havoc if you're using the contactor to supply fluorescents.
 
why not just fit a PIR to switch the lights on, leaving the manual switch in parallel. that way the lights will come on if you enter by the back door as well.
 
Thanks guys.

I am going to re-think this.

The unit does have a Triac.

The manual states in the specs "Triac 1A@230V"
So this is probably what controls the courtesy light as the lamp is rated at 40 Watts maximum although the manual does not say exactly what the Triac controls.

It's now a ---- up between the PIR and the limit switch, I shall have a think about this more but the main thing is not to damage the doors control unit so the Contactor wired to the courtesy light idea will have to go, it was a nice idea but too risky.

Thanks again people.
 
Last edited:
Well good luck whichever system you decide on.

All these systems with triac operated lamps are going to be problematic when they phase out incandescent lamps. CFL's and Led lamps don't mix well with solid state switches.
 
Also am I right in saying the collapsing magnetic field of the Contactor coil when switched off may induce a back EMF that could damage the Triac that is used for switching the courtesy light on/off?

A lot of questions I know but the subject's got me thinking.
 
Last edited:
Apart from the poor quality waveform the leakage through the triac can cause the filter capacitor on the input rectifier of a CFL to charge and discharge which cause flicker even when the lamp is supposed to be off.
The capacitive load of a CFL ballast can cause the triac to stop conducting prematurely and make it multiple switch during a single cycle.
The LC filter in the CFL also causes chaos when it encounters the rapid voltage swings of the triac output waveform. Similar problems occur with the EMI filters and drivers in an LED lamp as well although LED drivers are far more complex and the latest LED lamps have been redesigned to have some of these issues addressed.

There are certain ways around these problems but you have to take the lamps on a case by case basis. As a general rule for an easy life rather just avoid using anything but filament lamp in a circuit that's switched by a triac.
 
Last edited:
If you want a limit switch send me your address and I'll get you an old (but perfectly ok) one from work.
If the doors metal I'd use a proximity switch,that way you can set it a few mm off the top of the door so it never comes into contact with it like a limit does and won't wear out then but I doubt we've got any 240v switched ones,loads of 110v but your messing with transformers etc then,limit will do just fine.
 
I'll do a bit of reading this week, it's such a shame not to use the courtesy light, it really does everything I want, it has its own timer built in, it is right next to the board and it operates at 230 Volts, connecting the wires to a relay would be so easy.

It illuminates when the garage door starts to open and stays on for two minutes then switches off, perfect for what I want.

For a limit switch to do what I want it would have to be at the bottom of the door where it could be kicked or damaged, an optical device might be a safer bet you know the ones with a mirror, as soon as the door opens the beam is broken and hence the lights switch on, I could couple this with a timer and Bob's your uncle.

One other option would be to use the power to the motor as a feed to trigger a relay, as soon as the motor kicks in the lights come on, but when the motor stops the lights would switch off, maybe there is a device that can use the motor current as a trigger and then stay on for two minutes whether the motor has stopped or not.

This is entering into the realms of electronics, something I haven't studied in ages.

I just want the lights to operate when the door starts to open not when it is fully open and I want the lights to stay on for two minutes then switch off.

I shall let you know how I get on, maybe I will just give up and fit a PIR
 
Last edited:

Reply to Contactor Conundrum. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
636
Furthermore, as the left hand switch will currently not do anything, I'd try the loose brown in here:
Replies
4
Views
331
  • Question
There should be. Keep them all straight, insert two and then the third - don't twist them all together. If that doesn't work for some reason, use...
Replies
3
Views
1K
I'm just trying to understand the current your suggested relay needs to handle. Surely the above is not the running current of the lamp? That...
Replies
2
Views
191
Back to the Men's Shed today to complete the installation of the 4 LED battens in the attic. These were a joy to fit, having screwed the units to...
    • Like
Replies
0
Views
103

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks