When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains isolator. Or do I need to 10point check the mains isolator and then another 10point check on the contactor before removing.
Many thanks
 
TL;DR
Contactor. Proving dead. Which points to check. 3 phase
Why does it sound like an exam question to me??

As above, if you’re likely to use a screwdriver on a terminal, use a tester first.

Energising coil may not be 230v, but still test.

Mark everything with tape if not already labelled…. As everything is more than likely all the same colour of cable.
 
The industry standard method of making sure something is dead. Basically test every combination of phases, neutral and earth.
Thanks for reply. I just wondered if I must test the part to be replaced even tho I have tested mains isolator. Thsnks
 
Thanks for reply. I just wondered if I must test the part to be replaced even tho I have tested mains isolator. Thsnks
If you don't check at the item being replaced how can you be certain that you have turned off - AND LOCKED OFF - the correct isolator ?
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
 
Whats a 10 point check? how have i survived nearly 50 years in the industry without knowing this
If you have N cables then you have (N * (N-1))/2 pairs to check to know all are safe w.r.t. each other. So for:
  • Single phase (L + N + E) = 3 it is (3*2)/2 = 3 checks
  • 3-phase without N (just L1-3 + E) = 4 it is (4*3)/2 = 6 checks
  • 3-phase normal (L1-3 + N + E) = 5 it is (5*4)/2 = 10 checks
 
Last edited:
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Absolutely, the contactor control could be from a totally separate supply, maybe even UPS-backed!
 
If only the one source then just the isolator(s) but if unfamiliar with the panel/equipment or likely to have a further source, it wont hurt to double check the contactor too.
Brill thanks. If I was to double check at the contactor. Would you do the 10 checks again or just check the between the phases. Thanks
 

Reply to Contactor. Proving dead . 3 phase . in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

View: https://www.youtube.com/watch?v=glsg2HpWyok
2
Replies
21
Views
932
You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top