I have a DOL starter (https://docs.rs-online.com/c08c/0900766b81586106.pdf for reference) that I want to connect to my ac motor. I understand that the dol starter has a built-in contactor. I want to connect two other switches, a tilt and a proximity switch. Is it possible to connect these two switches to this DOL? If not how would I go about this?
 
I have a DOL starter (https://docs.rs-online.com/c08c/0900766b81586106.pdf for reference) that I want to connect to my ac motor. I understand that the dol starter has a built-in contactor. I want to connect two other switches, a tilt and a proximity switch. Is it possible to connect these two switches to this DOL? If not how would I go about this?
This video should help, form 15;00 mark onwards

Simply put a start device can be on parallel with existing, a stop device MUST go in series.

You just need to check if these additional switcheswpuld be Normally Closed (NC) or Normally Open (NO) in operation - If they're devices to interrupt operation they will likely be NC in operation (Opening if tilt or person proximity is detected or (in the case of a deadman style proximity - closing in the presence of a person and opening (stopping) if the person walks away)

 
What voltage is the contactor coil?
What voltage are the contacts in your external detectors / controls rated for?
Is there any machine safety functionality related to these controls and if so, what do your risk assessment and IEC 60204 (amongst others) say about that?
 
As lucien points out here we would need a lot of info before we could advise crucially the function of the motor and the underlying reasons for fitting the stop circuit limits.

Your profile suggests you are not qualified in the electrical industry so as a forum we have to be careful that any advice given reflects such, we may indeed be able to give guidance and help here but it does come down to what you are attempting to do, why and on what.
 

Reply to Contactor to DOL starter & switches in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
685
  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
748

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top