Hi again, just considering whether I'm going crazy or I've got a duff RCBO. Perhaps someone will help me see the light either way. Quite prepared for the former!
Installed it yesterday and when I got to doing the certificate I couldn't get it to trip. It's one of the ones with no earth wire. Took it home to test at my place and same.
L&N IN connected correctly, but whether I do a 0.5xI, 1xI, 5xI or ramp test, it doesn't trip at all (Megger 1552).
This behaviour whether load connected or not. Also noted that voltage at the input terminals is 236V and at the output terminals is 228V. Test button works as expected.
Just want to know I'm not doing something stupid before taking it back for a replacement.
Cheers