R

robsparx

I've done some work in a house, tried to test it, but the rcd trips out when i do an earth loop and when i do rcd tests (at half, 1 and 5 times)

I bypassed the rcd to get a result for my earth loop test, but the rcd test is still a problem.I ordered a new rcd, fitted it, and I'm still getting the same problem

the rcd is a contactum 80A 30 mA about a year old. just before contactum apparently changed their CU design

has anyone else had trouble with contactum rcds?
 
I think that after changing the RCD I would probably try and borrow a mates RCD tester to rule the test equipment out. I say this because going back many moons I had a fluke RCD tester that did not get on with Hager RCD's.

Just a thought ;)

It could also be a crossed Neutral in the consumer unit either from the house circuits or the Neutral links inside the the consumer unit itself. Does the RCD hold when a load is applied?
 
Last edited by a moderator:
Stating the obvious and not patronising,but can you confirm the loop tester has a no trip function, that was used and is working
A standard loop tester such as mine will not give a reading when testing via the rcd before out it goes as normal
Was half test done with all loads disconnected and carried out at source
Seems to be unlikely to be two rcds that are at fault but still possible I suppose
 
i think i'm going to borrow a mates tester and try again. i was testing a different job on friday, and the rcd test kept tripping out at half times aswell. although i could get my loop readings ok.

my tester does have the 'no trip' function. its a megger 1552, about 6 months old

Cant remember exactly off the top of my head now, but on the rcd were a couple of ring mains, cooker, normal domestic stuff really
 

Reply to Contactum RCD problem in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
853

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top