Hi, I've got a practical exam for testing and inspecting later this week. I've researched the net and these forums and there is some good info just need to get some things clear in my head so I'm certain about the testing for the motor circuit. Its single phase and the circuit goes as follows:
DB > ISOLATER > DOL > REMOTE START/STOP > SIMULATED MOTOR (NEON INDICATOR)
For continuity is it correct to be thinking:
1 - link out L-E at the board and get reading at the DOL
2 - get reading from the DOL to the motor (I'll need to link L-E somewhere here too?)
3 - add the 2 readings together for my total R1 + R2 reading
For IR, I test from:
1 - DB > DOL
2 - DOL > MOTOR
The thing I'm not sure about is where to test for the IR and if any connections need removing. For DB > DOL do I remove L-N-E at the DOL and test at the DB. For DOL > MOTOR do I remove any connections supply side of the DOL and test at the MOTOR?
Any help is much appreciated, thanks.
DB > ISOLATER > DOL > REMOTE START/STOP > SIMULATED MOTOR (NEON INDICATOR)
For continuity is it correct to be thinking:
1 - link out L-E at the board and get reading at the DOL
2 - get reading from the DOL to the motor (I'll need to link L-E somewhere here too?)
3 - add the 2 readings together for my total R1 + R2 reading
For IR, I test from:
1 - DB > DOL
2 - DOL > MOTOR
The thing I'm not sure about is where to test for the IR and if any connections need removing. For DB > DOL do I remove L-N-E at the DOL and test at the DB. For DOL > MOTOR do I remove any connections supply side of the DOL and test at the MOTOR?
Any help is much appreciated, thanks.