andy, i don't think it's a question of him not having done the calcs., but more that he needed to know what the question wanted.
 
Well I covered insulation resistance testing in one of books but I don't remember having to use that formula. I'll have to recap

Andy, well spotted. It should have been a 5 in my original post
 
Just a reminder that the final figure will always be lower than your lowest original value when doing parallel calcs like this - just a quick way to check and make sure you haven't gone obviously wrong somewhere.
 
thanks everyone for the help

So, I’m supposed to say what action should be taken if any.

Apart from the obvious safety precautions and use of correcttester and correct voltage I cant think of anything else to add.

The reading seem ok?? they are quite varied but I think that’snormal within different circuits

They are all above 1megaohm
 
thanks everyone for the help

So, I’m supposed to say what action should be taken if any.

Apart from the obvious safety precautions and use of correcttester and correct voltage I cant think of anything else to add.

The reading seem ok?? they are quite varied but I think that’snormal within different circuits

They are all above 1megaohm

I think personally, although the guidance states anything less than 2ohms should be investigated, I'd probably investigate a reading as low as this.
 
I think personally, although the guidance states anything less than 2ohms should be investigated, I'd probably investigate a reading as low as this.

TUT TUT, HT, you left the Meg out. :tank:
 

Reply to continuity clarification in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
714
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
304
Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
910

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top