Is the correct method for testing the continuity of the main bonding conductors with a long flying lead from the tester to the other end of the cable?
 
r2 is the earth path, with r1 being the resistance of the phase conductor.
with main bonding only the r2 is present

I think he wants to know why earth is called R2? not what is the R2?

The simple answer is because it is. Why is the phase conductor called R1?
I think it's because of the test that gets done ie. R1+ R2 which is your earth fault loop impedence test. If your circuit has a fault then the fault current travels down the cpc, which is what it's designed to do. You're therefore testing the impedance (resistance) of the phase conductor and cpc. hence R1 + R2.

I hope that makes cos it doesn't make sense to me.....:D
 
Last edited:
R2 Yes it makes sense when used in the earth loop impedance terminology.

But to call it R2 when refering to the individual conductor can confuse.
 
Last edited by a moderator:

Reply to Continuity test of protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
658
loz2754
L
I have a 13v AC transformer, to which wire numbers should I connect it to without destroying the windings. This was an old arc welder with a...
Replies
2
Views
455

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top