Hi, I have installed a small ring circuit which on continuity tests gives a problem. Rl,Rn and R2 all give acceptable readings of 0.6, 0.6 and 1.1 ohms respectively. Rl + Rn fine 0.04 ohms but as soon as I test Rl + R2 I get >200, which to me suggests an open circuit. Cable and sockets have been replaced but still with same results.
Any suggestions ?
Happy days Bob
 
Have done, all tests in order dead and live, socket tester proves ok and supply works without problems. The meter is brand new. Maybe I should check out the meter. Thanks for you help,
 
hey bob!! are you using the Plug on the test leads to test the circuits after setting up for R1R2...!! reason i ask this is i have same meter and when i set up for it and go round the socket fronts with the lead with the plug on i have to place Red End to Red Connection on meter and GREEN end to BLACK connection on test meter and leave the Black one disconnected..!

:)
 
As Durham said, make sure you swap the leads on the tester so that continuity is between R1 and R2, this is the most common cause of this if you are using a 3 lead tester or a Banana lead with a Plug.
 
last post seems to be the answer. can't comment on di-log though as i use megger. DOH, missed 3 posts. was meant to be answer re connection of leads
 
Last edited:

Reply to continuity test problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top