Testing a lighting circuit with a long lead, all readings R1 R2 Rn around 0.6 to.08 ohms. Adding R1 + R2 = more than 1 ohm. Is this acceptable for recording as the result or should it be less than 1 ohm. TT system.
Thanks for any advice
 
Nothing wrong with the reading being in excess of 1ohm at all as long as it tallies up with the theoretical calculated length.

As a rough guide you could check your results against the published resistance values for various cable sizes in the OSG.

Bear in mind they wont be identical due to a number of factors but it should give you a rough idea.
 
Thanks for the quick reply. Had already checked cable length against OSG table ohms/m everything was fine so thanks. Only a novice so needed reasurance. Thanks again.
 

Reply to Continuity Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top