I am wiring up a new kitchen and conservatory.

I'm not sure why I checked continuity between line and the metal back box of the light switch, but I did. I haven't even finished the first fix and the metal back box does not have an earth connected to it yet. The voltage tester (on resistance setting) beeped to show continuity. I then tested with the megger (IR test) and got 0.02Mohms. I can't fathom how there is 20000ohms of resistance between line and an unearthed metal back box?

This was at the end of today, I was (am) tired so I don't think my brain is in good detective mode. All I can think of is somewhere in that wall a screw has gone through a cable and is making contact with the line? Any other ideas?
 
I suspect you are IR testing the mass of earth through a damp wall to a metal box, rather like a poor earth electrode.
I'm guessing that even though line is not energised there is a path somewhere through a load to a N bar and back to real earth whether at cut out or further afield.
Is that plausible?
 

Reply to Continuity where you would not expect continuity! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
445
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top