This is an existing setup and I am wondering whether to modify it. It's not easy to get at so if I don't need to, I won't. I'm not sure if it will become part of the fixed wiring or whether it will be connected via a 13A plug, probably the latter, but basically we have a 370W (1/2hp) cap-start single-phase induction motor driving a pump, and a small DC power supply, controlled together by a 20A DP switch with indicator about 20 feet away. The supply arrives near the motor and feeds a double 13A socket outlet fixed to the chassis, but with a switch-cable in series. The motor and power supply plug into the two sockets. The switch cable is 3-core H07 with line, neutral and SL, the neutral being for the neon in the switch. Obviously, only one pole of the switch is used, so turning it off is akin to turning off the SP switches on the sockets themselves.
Doing it from scratch, I would put a normal contactor starter near the motor and run ELV control to a button station. However this is in situ and working, and for various reasons it's difficult to alter. The motor ought to have a motor circuit breaker / manual motor starter which can easily be added adjacent to the motor. No moving parts are accessible without the use of tools and there is no specific hazard from unexpected restart so I don't think it needs no-volt release. I wonder whether the switch is officially rated for very light AC3 duty - maybe one start per day? What about SP vs. DP?
Any thoughts?
Any thoughts?