Hi Everyone,

I need some advice on heating control circuits please.

I have 6 single phase 2kw infrared heaters which are fed from 6 individual 15A circuits on a 3 phase distribution board. Each circuit then goes to a local switch next to each heater and then on to the heater itself, and is currently controlled using the local switches.

I now need to be able to control all 6 heaters using 1x 7 day thermostatic timer. I am assuming that the best way to do this is to install contactors next to the distribution board, run each circuit from the distribution broad, through the contactors and then onto the local switch (which I will be retaining in case local switching is needed) and then onto the heater itself. With the contactors controlled using the

My question is: Do I need to switch both live and neutral in each circuit (3x 4 pole contactors) or can I just switch the live in each circuit? (2x 3 pole contactors.)
 
7 day timer Control the D/B with 1 suitably sized 4 pole contacter controlled via a 7 day timer through a fused single phase supply
 
That won't workfor me because the D/B supplies the power to the rest of the building, so if I switch the whole D/B I would loose power to the lights and sockets as well as the power supply to the control circuit.
 
I'm assuming that the 3P DB isn't specifically for the 6 heater circuits? If this is the case then you just need a small enclosure with 3 DP 20A contactors switching the line conductor of each circuit.
 

Reply to controlling heaters with contactors. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
514
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

You only need to switch the lines and the contactor is rated per pole so for example a 16A four pole contactor would be fine.
Replies
1
Views
334
I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
560

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top