Conversion to TNCS within property. A concern? And EICR code? | on ElectriciansForums

Discuss Conversion to TNCS within property. A concern? And EICR code? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 14, 2019
Messages
134
Reaction score
20
Location
London
Hi all

Have attached photo. Was inspecting property earlier in residential apartments and as you can see the supply has been converted to TNCS within the property and after the meter. This is the first time I have come across this before. I'm led to believe any TNCS conversion should be done before the meter as falls on suppliers side of responsibility. Would this be a concern to you? Would you code it?

Thanks
 

Attachments

  • [ElectriciansForums.net] Conversion to TNCS within property. A concern? And EICR code?
    IMG-20201130-WA0000.jpg
    85.6 KB · Views: 149
I would speak to the supply authority as that does not look right.At you say the PME should be done at the cut out. Is that cable in metal conduit that has been cut off as for the EICR I would give it an FI at this stage
 
ESQCR s8(4)
A consumer shall not combine the neutral and protective functions in a single conductor
in his consumer’s installation.

And I think I'd have to C2 that.
 
ESQCR s8(4)
A consumer shall not combine the neutral and protective functions in a single conductor
in his consumer’s installation.

And I think I'd have to C2 that.
Although, having just thought about that one for a few minutes, it actually reads going the other way around - so going from seperate Neutral and EC to a CEN/PEN. This is also reinforced by 543.4 and GN8 says nothing. Which therefore means no code ?.

I'm also slightly confused, given that TN-S is relatively rare for domestics, as to how they've ended up with just LN in the first place. Definitely need some pics of the intake and meter to make sense of this.
 
I have seen this a few times in large blocks of flats where it’s been converted in the mains room and just done that way in the flats .
That's as part of a BNO system under different rules. Ryefield boards have a removable link in them between the incoming N and a PEN arrangement to create TN-C-S, the same as in a DNO PME head.
 

Reply to Conversion to TNCS within property. A concern? And EICR code? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
687
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
875

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top