eagleeye
I went to a customers (a friend) house today to inspect a faulty oven. He said that the mcb kept tripping so i disconnected the oven and turned circuit back on. It stayed on for about 30 seconds then tripped with quite a big bang. I did and insulation resistance test on the circuit and between all conductors i got the same reading of 0.01 meg ohm. A dead short somewhere ? I have had something like this before where the cable had a jb on it and was laying on a wet floor below floor boards. could this be the case of this fault ? Think so.on a little further inspection the 6mm t + e cable that is on a 45amp mcbis actually suppling a 5.5kW oven and a 5.5kW electirc hob. not good me thinks. I am now gonna renew circuit and put in 2. on for oven and 1 for hob. i can drill straight though the wall under stairs to outside and run along 8 metres and go back though the wall to double pole switches in kitchen. W Normally use 6mm t + e but was just looking on a website regarding cable capacties and its saying that 2.5 will take about 30 or so amps. this cant be right can it. I thought 2.5 was about 18 - 20 amp, 6mm 30amp and 10mm 50amp. below i have put the link to what it says on the web site. Let me know your thoughts
http://www.eland.co.uk/documents/SWA Cables - BS5467.pdf
page 4
http://www.eland.co.uk/documents/SWA Cables - BS5467.pdf
page 4