Hi guys, firstpost here and would be really grateful for some clarification:
I am helping a friend install his new kitchen which includes installing a newoven and induction hob (links below).The existing oven was on a dedicated radial circuit with 6mm twin andearth cable, 32 amp breaker and cooker isolation switch.
The total loadrating of the hob is 4.6kw and the oven 3.68kw.I have been advised that allowing for diversity the existing cable is sufficientand to use a dual cooker outlet plate to connect the oven and hob.
The only aspectI am struggling to understand is what stops the hob or oven trying to pull thefull 32 amps in the event of a fault if the appliance is switched off?I’m guessing neither are designed to drawsuch amperage and with the breaker not triggering the full load is exceeded, would the hob or oven notpotentially catch fire?
Your inputwould be much appreciated.
Andy
http://m.johnlewis.com/mt/www.johnlewis ...age_loaded
http://m.johnlewis.com/mt/www.johnlewis ...age_loaded
I am helping a friend install his new kitchen which includes installing a newoven and induction hob (links below).The existing oven was on a dedicated radial circuit with 6mm twin andearth cable, 32 amp breaker and cooker isolation switch.
The total loadrating of the hob is 4.6kw and the oven 3.68kw.I have been advised that allowing for diversity the existing cable is sufficientand to use a dual cooker outlet plate to connect the oven and hob.
The only aspectI am struggling to understand is what stops the hob or oven trying to pull thefull 32 amps in the event of a fault if the appliance is switched off?I’m guessing neither are designed to drawsuch amperage and with the breaker not triggering the full load is exceeded, would the hob or oven notpotentially catch fire?
Your inputwould be much appreciated.
Andy