Hi working at a house and noticed the cooker cable (6mm) has been joined above the kitchen units to a 2.5mm which then runs into a fused spur and to the cooker, circuit has been on a 32amp mcb all this time, I was thinking to just put the 6mm on a 16amp mcb in the fuseboard and note it on the test certificate that the cable has been downsized.. what are peoples views on this? and where would it be best noted on the certificate?
 
How has the cable been connected at the transition from 6mm to 2.5mm???
 
Wouldn't an FCU count as your over-current protection for the 2.5mm cable meaning the 32A mcb is not ideal, but legal? Or am I getting my wires crossed?
 
Yeah, but I thought you could have over-current protection, as in an FCU, downwind of the change of cable because it's still protecting the 2.5mm no matter where on the route it sits?
 
it would just be two fused spurs in a circuit

What about the cb at the CU? if the fcu at the junction were to go open circuit and if it is not very accessible the the next sparky who comes in when the cooker is not working will find the cb OK but no 'juice at the cooker end, now that would be a head scratcher wouldn't it? rewire the whole circuit to be safe.
 
Last edited:

Reply to Cooker Cable Downsized halfway through circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
697
  • Question
Thanks for your time and opinion.
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top