Hi to all
Just wanted to get some opinions if poss. Im doing a kitchen electrics instal at the moment.
The hob that has arrived is rated at 7500watts and the the oven is a combination oven/microwave and is rated at 1000 watts.
There is an existing 6mm t & e circuit in place backed up by a 32 amp mcb.
So loading requirements at 230 volts foe the hob is 32amps
oven is 4.3 amps ish
would you folks tend to use the 6mm for just the hob and take s/f/spur off the ring for the oven?
Im half tempted to run an additional 6mm radial from the board for the oven so as not too push the ring to much and also for future if the oven is changed for a higher rated unit.
Thanks for reading
Just wanted to get some opinions if poss. Im doing a kitchen electrics instal at the moment.
The hob that has arrived is rated at 7500watts and the the oven is a combination oven/microwave and is rated at 1000 watts.
There is an existing 6mm t & e circuit in place backed up by a 32 amp mcb.
So loading requirements at 230 volts foe the hob is 32amps
oven is 4.3 amps ish
would you folks tend to use the 6mm for just the hob and take s/f/spur off the ring for the oven?
Im half tempted to run an additional 6mm radial from the board for the oven so as not too push the ring to much and also for future if the oven is changed for a higher rated unit.
Thanks for reading