P

phil333

Hi guys.

We have been brought into a domestic installation to complete remedial works. The previous electrician who worked for a builder was not very competent in his work and also could not sign off any of his work. He wired a new extension which included a kitchen. The council has been bought in to complete a certificate but has flagged up remedial works to be completed before he completes his test.

We have changed his new split load board to a new amd3 split load board, and have come across a fault.

The cooker circuit has a live cpc (floating voltage) but doesn't trip the MCB or the RCD.

When the dp cooker switch is off the voltage between the cooker cpc and the MET is 110V, when you turn on the dp switch it becomes 230V. The scary thing is, that when you connect this cpc to the MET the voltage drops to 23V but doesn't trip anything!

All the above tests have been complete when all other circuits are off. Polarity is correct in the cooker switch, insulation resistance test shows 299 to each core from the CU to the cooker outlet. No continuity between any cores either. r1+r2 readings are 0.11ohms, zs (when cooker switch is on) is 0.23ohms. RCD times are within the time limit.

Note : green gunk has been found in the conductor of the cooker circuit, which I have heard can cause issues...

Has anyone had this issue before as it's boggling my brain. The circuit has been isolated until the problem has been resolved.

Many thanks
 
Measured with a multimeter, that is what you would expect with a floating CPC in T+E. It's sandwiched between L & N and capacitive leakage will take it to a voltage somewhere midwayish. Not indicative of a fault.

Also not specifically indicative of a fault, just means that the cooker leaks much more to L than N. Even sound elements do tend to leak, test the cooker separately.

Not scary at all, but wrong. If the CPC is connected to the MET, the voltage between them is by definition zero, so I don't know what the 23V represents. I wouldn't expect anything to trip.

I'm not saying there isn't a fault but if you're testing with a Hi-Z meter, everything you describe sounds normal to me.
Bow to your superior knowledge Lucien, but can't understand how OP's MFT is conducting Zs & RCD tests, with all those ghost voltages knocking about, or is that not the case with all digital MFT? Would it be an idea for the OP to use an analogue meter to check voltages?
 
It will only be digital multimeters that show this problem (due to the very high input impedance which allows them to take measurements on very sensititive circuits). MFTs, even though digital, should not show this problem. Some people interchange multimeter and MFT though, which can confuse things :) Daz
 
Bow to your superior knowledge Lucien, but can't understand how OP's MFT is conducting Zs & RCD tests, with all those ghost voltages knocking about, or is that not the case with all digital MFT? Would it be an idea for the OP to use an analogue meter to check voltages?

Thats what I thought Midwest, but after using an analogue meter to check for voltage and reading the responses from the thread below (see posts 21 and 22) I feel happier with the drummond.

http://www.electriciansforums.co.uk...-odd-request-regarding-phantom-voltage-2.html
 
My Megger MFT will not allow me to do continuity testing if it detects ghost voltage.

Job today and a lighting circuit done in pyro but no earth continuity. MFT was telling me 100v between pyro sheath and MET.
Stuck my fluke indicator on it and was showing 12v. Get a bit of a tingle when you touch the two :yes:
 

Reply to Cooker circuit fault. Live cpc! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
773
  • Question
I recall where a fluorescent capacitor would cause a separate socket RCD to trip when turning off the light
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top