Need a little help here, never done seperate hob an Oven before.
Just been asked to look at a job for a friends Dad who was brought a ground floor flat.
He has taken out his old cooker and wants to replace it with a seperate Oven and Hob.
Oven - 2.1KW
Hob - 6.6KW
It is fed by to a cooker switch with 6mm cable with a 30A breaker (board is early 80`s)

If I feed from the cooker switch (no socket) to a JB can I connect both?
The Hob pulls 28A and the Oven 9A, Thats 37A on full load, working out diversity its 28A.
So I am thinking should I spur off the kitchen ring for the oven with a 13A plug or fused spur.

As he also wants to replace his shower and change a shaving socket to a light over the sink
I have suggested a new board with RCD as there is no RCD at present but he says he can not
afford it. I am going to have to put a seperate RCD in here anyway, special location etc.
There is little room to do much beacuse of all the storage heating controls. All hidden in a broom
cupboard.

Any help much appreciated
 
Hello all,

Need a little help here, never done seperate hob an Oven before.
Just been asked to look at a job for a friends Dad who was brought a ground floor flat.
He has taken out his old cooker and wants to replace it with a seperate Oven and Hob.
Oven - 2.1KW
Hob - 6.6KW
It is fed by to a cooker switch with 6mm cable with a 30A breaker (board is early 80`s)

If I feed from the cooker switch (no socket) to a JB can I connect both?
The Hob pulls 28A and the Oven 9A, Thats 37A on full load, working out diversity its 28A.
So I am thinking should I spur off the kitchen ring for the oven with a 13A plug or fused spur.

As he also wants to replace his shower and change a shaving socket to a light over the sink
I have suggested a new board with RCD as there is no RCD at present but he says he can not
afford it. I am going to have to put a seperate RCD in here anyway, special location etc.
There is little room to do much beacuse of all the storage heating controls. All hidden in a broom
cupboard.

Any help much appreciated
No you can't mate,anything over 2KW has to have it's own dedicated circuit.What happens on Xmas day when everything is going full load.Just use RCBOs on the circuits that need protected and note it on the cert.If the customer doesn't want the CU changed,you can only advise and note it again on the cert.
 
Thanks Mac,

Just so I understand, I need a circuit for the cooker and a circuit for the hob?
If thats the case this is not good news as it is a ground floor flat and the bathroom is between the
kitchen and the board, which is also on the far wall!
I don`t think I will be able to get a RCBO to fit this board, its an old ceramic Crabtree with MCB`s, what do you think of putting a RCD main switch in before the board, I saw this recently, I was not sure but from the feedback received it conforms.
 
Thanks Mac,

Just so I understand, I need a circuit for the cooker and a circuit for the hob?
If thats the case this is not good news as it is a ground floor flat and the bathroom is between the
kitchen and the board, which is also on the far wall!
I don`t think I will be able to get a RCBO to fit this board, its an old ceramic Crabtree with MCB`s, what do you think of putting a RCD main switch in before the board, I saw this recently, I was not sure but from the feedback received it conforms.
Main RCD switch is ok if the customer won't pay for an upgrade.How old is the installation.When you replace MCBs/rewireable fuses with RCDs,this is when the problems start.
 
from memory you can supply 2 items from the one switch as long as theyre no more than 2 metres from it. will look in the book later ;)
No worries mate.How many CUs are within 2 metres of the kitchen.Me personally would still run separate supplies for each appliance.Good practice in the long run:D:D:D
 
I dont see any reason why the oven (2.1 kw) cant be plugged into a single socket wired onto the kitchen ring circuit, PROVIDED it is a dedicated kitchen ring...and other heavy loads are taken into account, ie washing machine etc. I also dont see any reason why the existing cooker circuit cannot supply both appliances,but I wouldn't use a JB. A better arrangement would be to split the cooker lead coming from the isolator with a fixed adaptable box and large flex glands to secure the cables.A 6.0mm (will be fused at 32a) could feed a single socket to plug the oven into. Fully agree that if dedicated circuits can be installed so much the better,but with the loadings of the appliances given by Walec I dont think i'ts worth major upheaval to achieve.
 
Last edited by a moderator:
On a 6mm cable,you are jesting:eek:Separate supplies mate;)

No Mac, I'm not for one second sugesting you run 50 amps on 6mm cable,
I'm just quoting the regs which say that a cooker circuit can supply two cookers up to a rating of 50 amps.
Of course all the other factors would need to be in place such as cable size, procetive device, reference method etc etc.
 
Guys, Thanks for all your comments, the guy is on hoilday now until Monday, I will re-visit and take another look, I have just read in the Electricians Guide to the building regs (Green Book) that a lightly loaded oven of 13A or less may be connected into a ring final circuit. I will asess again though and let you know what I do. Cheers
 
Personally i dont see a problem with connecting the 2 cooking appliances to the existing circuit.

The 6mm cable is rated above 30Amps and the diversity brings the load within that.

This work would not need certifying or notifying as no work is being done on the fixed wiring.



Having said that, I would carry out a few quick tests on the circuit to make sure everything is in check, mainly for peace of mind.

It would be better to have a 40A circuit installed, however as long as the client is aware of the possible problems.
 
Last edited by a moderator:

Reply to Cooker + Hob in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
784
  • Question
Since my last post I have used the oven several times and it is still working ! On reading the 'regulatory' position I will ask an electrician to...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top