Does anyone know through 17th or building regs what are the min and max distances say a 45 Amp D/P cooker switch must be from the cooker.
I understand that the min is 300mm from cooker and to the side and must not be more than 2 meters away be visible accessible and in the same room as cooker for quick isolation. My supervisor agrees that that 300mm is min and goes on to say that it can be located anywhere?? Working on a multi million pound apartment and designers have put it in a cupboard about 4 meters from cooker. Have looked for definitive however just get recommendations suggestions and should not concrete fact.:cool:
 
differing opinions will be found from different members about the cooker control switch. it must be fixed to the fabric of the building the controversy is do fixed kitchen units count as the fabric of the building and can it be behind a cupboard door. personally ive seen and done both with no problems. it should be within 2 metres of the appliance though.
 
OK lets get shot down.

Ideally away from potential heat damage - 300mm is fine. Maximum distance? Well....

You do not have to have the pullcord switch (or any other switch) for a shower in the bathroom. I queried it once with the NIC ! I believe local isolation is a good thing but it appears NOT to be statutory because, possibly, you can turn the cooker off on its own controls.

Therefore you can put the switch anywhere as long as there is a means of isolation.

Anyone got any labels......? :D
 

Reply to cooker isolaters position in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
582
  • Question
No offence meant, if your suitably qualified, then that's that. As regards certification, I note that this work is being done as part of an...
Replies
28
Views
5K
M
Replies
4
Views
9K
mrpinky
M
S
  • Question
Thanks. And I've calmed down as well...
Replies
6
Views
3K
Scooby
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks