Old Gas cooker is being replaced with a cooker that has an electric oven and gas rings. Existing supply for gas ignition was via a switched fused spur from the ring. With cable then running diagonally (not exposed) to a flex outlet!

To run a new cable would be a very big job. Rating of cooker is 2900W. I know the regs suggest that cookers over 2kW should be on their on radials.

Existing SFS would be directly above the new cooker rings (cooker is wider). So my thoughts are:

a) Blank off existing SFS and keep ring continuity
b) Remove a 2g socket nearby (not over cooker rings) and replace with a cooker switch and run 4mm T&E in trunking to a point behind the cooker, into a flex outlet.

Should be OK?
 
That works out you could run that on a 13a plug top. So if you run 2.5 from a 13 switched FCU hey presto. But maybe not your old one as the position is right above the hob :)
 
Last edited by a moderator:

Reply to Cooker supply from ring in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

Similar threads

  • Question
Thanks so much for all the responses guys! It seems that what I'm planning is nothing unusual or regs-busting. I'll hook it all up and have a...
Replies
7
Views
3K
  • Question
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
2
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top