Have come across a 10mm t&e supplied from 45a 60898 installed a/c. This runs into back of cooker switch back box- terminated into 45a connector blocks- then they have down sized to 6mm and supplied the supply side of the cooker switch -but the supply side has been doubled up with another 6mm supplying a near by single socket ref method a/c again.
then a 6mm from the load side of the cooker switch to a cooker outlet below.
from the cooker outlet- 1x 6mm supplying 4.5kw cooker and 1x 2.5mm (looks like factory flex) supplying a 8kw hob
I have added the kw's of both the hob and cooker together - took the 1st 10amps and remaining 30%
then I added 5amps (although the single socket is not actually on the cooker switch- but same idea I guess?
i got 28.3amps after diversity- so no problems on the overload side I guess.
all done fairly well to be honest when it comes to terminations- I am just not sure if I should pull up the 10mm into 6mm and the 2x 6mm doubled up in the supply side of the cooker switch although no cores appear to have been cut?
or am I just over thinking things here? Move on?
joe
then a 6mm from the load side of the cooker switch to a cooker outlet below.
from the cooker outlet- 1x 6mm supplying 4.5kw cooker and 1x 2.5mm (looks like factory flex) supplying a 8kw hob
I have added the kw's of both the hob and cooker together - took the 1st 10amps and remaining 30%
then I added 5amps (although the single socket is not actually on the cooker switch- but same idea I guess?
i got 28.3amps after diversity- so no problems on the overload side I guess.
all done fairly well to be honest when it comes to terminations- I am just not sure if I should pull up the 10mm into 6mm and the 2x 6mm doubled up in the supply side of the cooker switch although no cores appear to have been cut?
or am I just over thinking things here? Move on?
joe