tigerpaul

-
Arms
Joined
Nov 11, 2008
Messages
403
Reaction score
105
Location
Tadley
Right then, I'm putting a new circuit in for a 12kW cooker

12000W / 230V = 52.17 amps

That would be the full load current, and I need a cooker switch that is capable of switching the full load current right? (BS 7671 regulation 537.3.2.5)

So as most cooker switches I have found are rated only at 45A that leaves me a problem, what kind of switch can I use?

Any ideas fellas??
 
Hi Tigerpaul

Once you apply diversity to you figure (52.17 amps) you will come in well under the 45 amps of cooker switch

Diversity for cookers is 10a +30% of remaining current
 
Now at college, we were taught you apply diversity to all your maximum demands of individual circuits so you can calculate the total assumed current demand of the submain.

This was because it is unlikely that all the lights, all the sockets, the shower, the cooker, everything would ALL be on at the same time.

Quote from The Electricians Guide to the 17th Edition by John Whitfield:
"At Christmas it is likely that 2 ovens all 4 hotplates and a 3kw ketle could be simultaneousely connected. Just imagine the chaos that a disconnected cooker circuit would cause! This alone is a very good reason for being generous with cable and protective ratings"

The cooker I am feeding has 6 hotplates, and I dont know why anyone would install one unless they did need to use many hotplates at the same time (big family/did a lot of entertaining etc)

This brings me back to my original question, where do I find the cooker control switch that can break 52.17A ?
 
Yes rating you state is if you were to theroetically put all the hot plated on full, turn the oven upto max setting etc, it would still not be drawing 53 A, generally the 30% diversity was arrived at after testing, the assumption is that if all the hot plates were switched as they are thermostatically controlled 1 would be taking full power, 1 would by switching on, 1 would be switching off, 1 would be taking no power as it reached temperature etc etc, as a safety factor they added the 10 A to the equation. Same apply to the oven once it reaches temperature the power is switced off/ reduced.

It easier to see the principle on an gas oven, switch it on set it to say 200 C leave it on for say 20 mins, then open the door and look at the flame. high or low.

I beleive your article is on about cable sizing 10 mm or 16mm depending on installation conditoion lenght of run etc and install max size control unit
 
Last edited by a moderator:
What kind of premises is this cooker going into, ive noted with commercial and industrial kitchens they often use an appropriate isolator with a 60amp or 63amp been a common size.
 
Its going into a big house. They want this big six ring ceramic range.. So its not your average cooker.
I reckon on ten mil cable fifty amp mcb. But then the switch is only rated at forty five amps, which concerns me a bit.
 
Off topic a tad but i have just installed a new double oven at a clients property.

I turned the main oven on (full) and clamped the line conductor.

It was only drawing around 8 amps from cold, including the fan.
 
RangeMaster supply domestic cookers at up to 15Kw. In the RangeMaster iinstallation material it specifies a 45A switch (allowing for diversity). The Regs generally allow an installation to be guided by the supplier's recommendation (assuming it's an, er, reputable supplier).

You should be fine with a 45A switch. The cable size will depend on other circumstances such as length and routing.
 
It's gonna be 10mm2 T+E, 50a mcb and 45A cooker switch. Its run on its own, no insulation.. Should be fine. My only worry is if the switch can handle it when it's on full load.
Zupos reckons the elements will be cutting in and out as the cooker reaches and then maintains temperature, so hopefully it shall be fine...
 

Reply to cooker switch for 12kw cooker in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top