Put a cooker feed in in 6mm three core SWR (armour) run on otside of building. I earthed the armour screen but did not use it as part of the earth path. The suppliers feed is TNC-S
cable run 12Mtrs aprox plus 2 mtrs 6mm T&E.
Using a Fluke 1653 checked Zs for certificate and I get a reading of Zero Ohms. Is this to good to be true
I checked and re zeroed meter still the same. checked it against a ring main socket and got what I would expect.
Test done on the open T&E tails before connection.
Any sugestions would be welcome.
Mike