Hi chaps.

Put a cooker feed in in 6mm three core SWR (armour) run on otside of building. I earthed the armour screen but did not use it as part of the earth path. The suppliers feed is TNC-S
cable run 12Mtrs aprox plus 2 mtrs 6mm T&E.
Using a Fluke 1653 checked Zs for certificate and I get a reading of Zero Ohms. Is this to good to be true
I checked and re zeroed meter still the same. checked it against a ring main socket and got what I would expect.
Test done on the open T&E tails before connection.
Any sugestions would be welcome.

Mike
 
Last edited by a moderator:
Hi, have you done an earth loop test after connection? You could do this at the cooker socket and get a realistic reading - I can't see how that length of cable could give a zero reading. I've used a fare bit of SWA recently and although its good, it can't be that good. If nothing else you should get some resitance on the short length of 6mm T+E. I assume the fluke shows that you have a continuous circuit - I've never used one but my megger shows whether it is continuous or not. I would connect the CU end Phase/CPC and give it another go -if still nothing then resort to live tests after connection. Hope this helps a bit.
 
Hi ElectricMick.
Thanks for your reply. I was begining to think there was no one out there.
The Zs measurement I took was on the live circuit Live. Every thing seems to be ok with the other tests, ins resistance etc it was just this one reading that was throwing me, it seemed to good to be true. I can only assume my meter was playing up on the Zs test.

Mike
 

Reply to Cooker Zs zero 0hms in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
I have replaced the back box for a 35mm one, and it all has refitted more comfortably. I'll get the electrician to check it out when fitting the...
Replies
2
Views
953
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top