my boss has asked me to work out the design current for a 10.8Kw 3 phase cooker for a commercial kitchen...
Now then....according to the osg (p97) table 1b column 3 it states that its to be 100% full load then 80% for other appliances on this circuit. So 10.8 Kw equates to 47A so is that 47A spread across the 3 phases? He wants to use 4mm 5 core hi-tuff and a 32A tripple pole MCB....
Now then....according to the osg (p97) table 1b column 3 it states that its to be 100% full load then 80% for other appliances on this circuit. So 10.8 Kw equates to 47A so is that 47A spread across the 3 phases? He wants to use 4mm 5 core hi-tuff and a 32A tripple pole MCB....