Hi, I have a customer who has bought a 7Kw hob to compliment a 4.8Kw double oven. He didn't realise the extra power consumption would put additional loading on the existing 6mm cable. My initial response was to tell him that an additional circuit was required and due to locations of consumer unit and hob it won't be straightforward
However I looked at diversity regarding cooking appliances and 51amps loading reduces to 23 or 28 amps which is within the capacity of the existing wiring.
I will probably still go with the additional circuit but what's the point of having diversity if we don't apply it. Thanks for your thoughts.
However I looked at diversity regarding cooking appliances and 51amps loading reduces to 23 or 28 amps which is within the capacity of the existing wiring.
I will probably still go with the additional circuit but what's the point of having diversity if we don't apply it. Thanks for your thoughts.