Ive got a copy of this table, but not sure where it was derived from?? Has anybody else seen/used this table??
 
Throw it away it's wrong!! All SWA cables from 2 core to 4 core up to 95mm will comply with min CSA for use as the cables CPC. Main bonding requirements is a different matter, and should not be confused with sole use as CPC...

Copper has a conductance of approx 8 times that of steel...
 
Here use these two tables, tried tested and proven... lol!!


Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

15

16

17

2.5

5.7

17

19

20

4

9.0

21

23

35

6

13.6

24

36

40

10

22.6

41

44

49

16

36.1

46

50

72

25

36.1

60

66

76

35

36.1

66

74

84

50

56.4

74

84

122

70

79.0

84

119

138

95

107.2

122

138

160

120

135.3

(131)

150

220

150

169.2

(144)

211

240

185

208.6

(201)

230

265

240

270.6

(225)

(260)

299

300

338.3

(250)

(289)

(333)

400

403.9

(279)

(319)

467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.


Conductor CSA

Minimum CSA of SWA to meet 54G

CSA of armour 2 core

CSA of armour 3 core

CSA of armour 4 core

1.5

3.4

16

17

18

2.5

5.7

17

19

20

4

9.0

19

21

23

6

13.6

22

23

36

10

22.6

26

39

43

16

36.1

41

44

49

25

36.1

42

62

70

35

36.1

62

70

80

50

56.4

68

78

90

70

79.0

80

90

131

95

107.2

113

128

147

120

135.3

(125)

141

206

150

169.2

(138)

201

230

185

208.6

(191)

220

255

240

270.6

(215)

(250)

289

300

338.3

(235)

(269)

(319)

400

451.0

(265)

(304)

452
















 
Last edited by a moderator:
Just noticed, that table you posted is relating to ''Thermal Setting insulation'' cable operating at 90 C, which you can count on experiencing once in a blue moon. The thermal setting insulation cable table in my example, has beeen suitably adjusted to operating at 70 C. Not that you'll probably ever see a typical SWA cable operating even close to that sort of temperature either!!

That above table is like the wirenut table that's been doing the rounds since the late 70's, in being basically misleading, confusing, and pretty much useless for 99% of installations....

Anyway that's the reason why they are giving over the top values for min CSA to comply with table 54G.
 
Also and I know this should be bloody obvious, but make sure you still work out what the Zs is going to be at the end of the cable. Only really becomes an issue on longer runs.

The Armour is all well and good being a CPC, but if you can't meet disconnection times...
 
Also and I know this should be bloody obvious, but make sure you still work out what the Zs is going to be at the end of the cable. Only really becomes an issue on longer runs.

The Armour is all well and good being a CPC, but if you can't meet disconnection times...
how would you go about calculating R2 of an SWA ?
 

Reply to Copper equivalent to SWA armour in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
197
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
248
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
346

Similar threads

yes it was a pee-take... I was commenting if someone was dumb enough to use earth clamps on armour, they might just be dumb enough to earth a...
Replies
6
Views
454
totally agree
Replies
12
Views
994

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top