Id like to run a 20m 4mm2 armoured to a log cabin/shed type thing!? On a 32amp mcb on an rcd C/U
Then have small garage type C/U in cabin but they always seem to come with 63 or 40amp rcds as main switch.
Not sure where i stand with discrimination. Just a few sockets and lights in cabin so a 16 or 20 for sockets and 6amp for lights
 
first, the 40A or 63A rating on a RCD is the max. load. nothing to do with tripping. secondly, it's not a good idea to have 2 RCD in series. replace the RCD in the sub-main with a 2 pole isolator feeding your 16A and 6A MCBs, or feed from the house independent of the house RCD, which may entail splitting the tails to the CU.and fitting a separate MCB to protect the SWA.
 
Oops wrote before last post looks like im going to have to split tails then.
What if the cabin main rcd was swapped for a 100 isolater,cabin would be rcd protected from house main rcd,not ideal but is it legal?
 
hang on. are you talking amps here or milliamps? the first is the load capacity and the second the trip current . and you don't want 2 rcds. if you are supplying via the house rcd, ditch the garage rcd.
 
Sorry i think i repeated what you said first ,ditching rcd in cabin for isolater,wasnt sure if this is ok thought cabin would need its own rcd but then would end up with them in series
 
oops, posts crossed.it.s not a problem to have the rcd in the house, but just an inconvenience -if a fault occured in tghe garage, it would take out all circuits on the house rcd.
 
right guys you aint reading the post correctly. the cu in the shed/cabin has a 63A main switch and he is asking how will this be with him feeding the shed/caabing cu with a 32A mcb
 
his main switch can be 1000A for all it matters. it's the MCBs that provide circuit protection. the rating of the main swith is just the current it can safely withstand.
 
Ha even im getting confused now, the garage c/u comes with either a 40 or 63 amp rcd feeding a 20 or 16amp and 6amp mcb. The house c/u is a 100amp rcd swich feeding other mcbs in house.I wanted to use a 32amp mcb fed off the 100amp rcd switch. I wasnt sure how i stood with this set up.
But i think we got there in the end by elimating the 63/40 amp rcd switch in garage and changing to standard isolater switch so: 32amp mcb (backed by main c/u rcd) to the garage c/u with isolater to 20amp&6amp mcbs.
 
maybe 100mA rcd covering whole installation in house. = s type i think.

anyway you shouldn't have two rcd's in line unless they are of different rataings (I an)
 
if the house CU has an upfront 100A, 30mA RCD, your problem is that a fault in the garage will take the whole house out. the ideal solution would be a new, hi integrity CU in the house, but cost may be an issue. if that is the case, i would split the tails and feed a 32A MCB in an enclosure, from the henley blocks and use the "garage board" with it's RCD and 2 MCBs. all you need to worry about then is adequate earthing!!!
 

Reply to Correct discrimination? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
190

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top