ukpablo
ok, without visiting the premisies and without testing the actual voltage, what is the score with this specific shower.
existing set-up
6mm T&E
40A mcb with rcd protection
old shower was 8.7kw load / 9.5 kw supply voltage??? so instructions read!
new shower, still in box
instructions state:
230 v 50hz etc 9.5KW (nominal voltage 240V)
8.8KW (nominal voltage 230V)
Both under 40A with calculation, so question is do i need to measure actual voltage, and what is the pwr the shower is rated at??????????? is it somewhere between??
Also i know 9.6KW should be 10mm T&E so is existing ok? i believe it is but that is why i am asking for some form of clarification.