Corroded swa gland - garage CU | on ElectriciansForums

Discuss Corroded swa gland - garage CU in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 19, 2016
Messages
82
Reaction score
38
Location
Preston
Hi,

Have a garage consumer unit supplied from the house CU via a 6mm 2core swa. I noticed this morning the gland entering the garage CU was loose so opened it up to tighten up the gland lock nut. Unfortunately it appears the gland as it enters the garage cu has corroded and brocken away from the lock nut. It's only been install 3 years and the other glands show no sign of corrosion. I have suspicions as to what has caused it but would like some other views on the matter. Pics attached. Thanks

[ElectriciansForums.net] Corroded swa gland - garage CU


[ElectriciansForums.net] Corroded swa gland - garage CU
 
That's what I was thinking. As you have probably already established, the swa is utilised as Cpc. As a consequence there is no separate dedicated bonding provided within the garage I.e. Earth rod / nest as this isn't required, however; one of the outgoing ways from the CU serves an external metallic lighting column. Could this accelerate the corrosion?
 
Thanks all, the CU is aluminium and I thought the gland was copper / brass. It's the gland which appears to have failed, in this instance at the point it passes through the Al CU. I can't have this happening again, who knows how long ago it actually failed. I'll investigate Al glands.
 
What else is connected to the earth bar?

Did you pull the shroud back from the gland? Was there any sign of moisture ingress?

Uncoated brass and nickle-plated brass glands are designed for use with dissimilar metals ie steel armour strands which are galvanised so I don't see how the gland having a galv nut would cause such advanced corrosion in such a short time.

If the CU enclosure material is ferric or steel based then moisture under the gland nut could cause it to rust, especially where the paint might have been cleaned off to ensure good contact for the earth ring. Rust causes expansion (think of windscreens that crack when rust gets under them on a car) which could have cause the gland to split.

It's worth noting that moisture around the gland could be caused from it dripping inside the enclosure but could also be coming from inside the cable sheath by capillary action. so I'd disconnect the armour at both ends and megger it to a known earth, if it fails then start digging to find the cable sheath damage.
 
I feel fairly sure the BG IP rated boards are cast alloy (not sure what alloy) not aluminium, the metal does not respond like aluminium and it would not be all that "non combustible" as aluminium is highly reactive (when exposed) and has a low melting point.
A current flowing or induced in the metal of the CU would increase the corrosion rapidly and I would agree with Marvo about the possibility of water in the shroud, though it does look like it is coming from above.
 

Reply to Corroded swa gland - garage CU in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
533

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top