GBDamo

-
Arms
Joined
Jun 22, 2016
Messages
1,911
Reaction score
3,015
Location
UK
The old landlord and owner has retired into the adjoining cottage. This cottage is fed from a 100 amp isolator that is Henley blocked off the meter tails from feed to the pub. The feed cable to the cottage is 16mm t&e and runs about 5-10m and feeds an old wilex rewireable fuse box. From a fuse in this board another 16mm t&e runs for about 10-15 m to a plastic non-RCD CU.

Assuming(I know) that the Ze and Ze at the CU are good I plan to swap two MCBs in the CU to run two new circuits in protected by compatible RCBOs.

Now if all tests ok I'm happy with the work I intend to do however I don't like the set up as is and have suggested that as a minimum he should look at some kind of additional protection in the form of an RCD.

Is this reasonable?

I'd look to put the RCD between the 100amp isolator and the original fuse box.

Other than nuke it from orbit, any advice.
 
Not sure how anyone connected a 16.0 T&E cable from the outgoing terminals of a Wylex standard board without reducing its csa.
It's a pub, would you expect the wiring to be done to any known logical standard?
 
Remove two unused MCBs from the wylex CU in the cottage and replace them with RCBOs for two new radial circuits.

This will depend on:-

1. The suitability of the earthing arrangement from the cottage back to the mains head.
2. Determining how bondable services enter the cottage and ensuring they are bonded.
3. The overall load for the pub and cottage Vs the mains fuse.

The upfront RCD was merely to ease my twitchyness about the whole set up but not really my responsibility.
 
Where is the water/gas fed from? If from the pub then there may be no requirement for bonding, but only testing will confirm this.
 
Where is the water/gas fed from? If from the pub then there may be no requirement for bonding, but only testing will confirm this.
Agreed, but if it's not present in the pub then work there would not be covered under my domestic installers scheme.

Like I said earlier, a potential right can of worms.
 
Agreed, but if it's not present in the pub then work there would not be covered under my domestic installers scheme.

Like I said earlier, a potential right can of worms.
I would say common sense should apply here however the schemes don't see it that way.
 

Reply to Cottage fed from pub next door. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K
  • Question
Interesting item you have there. This blog might be worth a read https://sllipblog.wordpress.com/2014/04/29/its-now-00-28am-and-i-need-my-bed/...
Replies
9
Views
612

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top