Went to some family friends earlier who are having nuisance rcd tripping problems.
They have just about every probable cause going - rusty freezer in a garage fed underground in non swa, underground feed to a shed in non swa, enough fridges, freezers and washing machines to put Currys to shame etc etc but a feeling that it is the oil fired central heating that is causing the problem, mainly because the frequency has been increasing since the end of summer.
I switched every mcb on the board to off and then tested the rcd on two seperate circuits. Test 1 was on a circuit that had the boiler, a dishwasher, a fridge freezer and a pump to fill a header tank with harvested water for toilet flushing. I was unable/unwilling to ir test this circuit as I didn't know what else may be on it and couldn't get to any isolators etc. The second test was using another rfc but with nothing plugged in and the 3 ir results were all 299+ MOhms.
Test 1 Test 2
.5 0 1999+ 1999+
.5 180 1999+ 1999+
1 0 300+ 300+
1 180 47 26
5 0 22 26
5 180 22 21mS
Ramp 21 24mA
I don't need a conclusion but an explanation! I have got out my pictures of how an rcd works but cannot see how it can be more sensitive on 1 cycle compared to another. Additionally I cannot see why a circuit which undoubtedly had some earth leakage on it already before my meter introduced more would take longer to trip (result 1 180deg) than on a completely clear circuit.
At the moment I am tending towards having a few beers to help me sleep unless somebody could explain please! Sorry if this is a basic question
They have just about every probable cause going - rusty freezer in a garage fed underground in non swa, underground feed to a shed in non swa, enough fridges, freezers and washing machines to put Currys to shame etc etc but a feeling that it is the oil fired central heating that is causing the problem, mainly because the frequency has been increasing since the end of summer.
I switched every mcb on the board to off and then tested the rcd on two seperate circuits. Test 1 was on a circuit that had the boiler, a dishwasher, a fridge freezer and a pump to fill a header tank with harvested water for toilet flushing. I was unable/unwilling to ir test this circuit as I didn't know what else may be on it and couldn't get to any isolators etc. The second test was using another rfc but with nothing plugged in and the 3 ir results were all 299+ MOhms.
Test 1 Test 2
.5 0 1999+ 1999+
.5 180 1999+ 1999+
1 0 300+ 300+
1 180 47 26
5 0 22 26
5 180 22 21mS
Ramp 21 24mA
I don't need a conclusion but an explanation! I have got out my pictures of how an rcd works but cannot see how it can be more sensitive on 1 cycle compared to another. Additionally I cannot see why a circuit which undoubtedly had some earth leakage on it already before my meter introduced more would take longer to trip (result 1 180deg) than on a completely clear circuit.
At the moment I am tending towards having a few beers to help me sleep unless somebody could explain please! Sorry if this is a basic question