Sean9461

hi,

I'm looking for some help in regards to working out the load calculation of a wire.

I'm pretty sure it should be ok but I just want to double check.

I have an outhouse workshop and have a mcb in my main house.

I had an electrician in to install a sub panel in the outhouse.

He installed a 10mm2 cable which only extends 3m max to the sub panel.

He installed a 50a breaker in my mcb leading to the sub panel.

The mcb has a rcd in it.

Now I'm aware about having to get an electrician in however my question is very simple.

The 50a breaker I would like to upgrade to 80a.

To run more load as I run a business from home several servers etc.

From all calculations I have done the 10mm2 cable over 3m should be able to handle 80a.

So I should be able to simply switch out the breaker for a 80a.

I would just like to confirm this with you guys. Can anyone confirm that this should be ok?

I really don't plan on paying or even getting someone to drive here to simply install a new breaker for me when it's literally as simple as switching a 3 pin plug.


Cheers
 
you can't fit a 80A breaker to a 10mm cable. 50A is the correct size. last time i saw a 80A on a 10mm was the morning after the Fire Brigade had attended. and it was bloody boxing day at a local cattery. poor buggers had no heating in the cages till after i'd been and sorted it asll out.
 
What is the calculation you use to work out the breaker size then?

As I used a website that works out the calculation for you and it came back saying over 3m at 10mm2 can carry 80a
 
I don't really know where to start, apart from, no you can't do what you are planning without it being dangerous.
Get an electrician in to do a load assessment for you and see what you actually require. If you really do need more than a 50A supply I'll be gobsmacked. If you do actually require a 80A supply out to your outhouse then it's probably time to contact the DNO to uprate your service cable.
 
You would be putting the property and its occupiers at risk if you do this!!! Why not get a local electrician in to upgrade the submain cable and breaker and give you the proper documentation for it?
 
As above, you need to get the job re-assessed, also another point is your incoming supply, have you contacted your supplier to enquire what allowance and DNO fuse rating you have, it may be that you have a 60, 80 or 100amp service fuse which may limit you.

I also ask you why you want to upgrade to an 80 amp, I suspect the rcd is tripping with all the servers designed earth leakage, was the Electrician made aware what type of loading was going on this circuit as I suspect this is designed wrong if that is the case, so can you confirm why you want to increase to a 80amp when from what you say, I find it hard to justify an 80amp supply for a few servers unless your running a big office block.
 
I may have worked out total load wrong.

I have a farm house and have a new extension on the outhouse which i plan on adding extra rings eventually as well to have a seperate flat for mother in law.

I'll get an electrician out then

Cheers
 

Reply to Could use some help with wiring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
2K
D
  • Question
Nail as a fuse works until it doesn't. When you say certain areas what does that mean? If you have been doing it like this for 4 years why the...
Replies
4
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top