couple of questions | on ElectriciansForums
Discuss couple of questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
N
nicsin02
awrite guys just a few wee questions
1. at work there is a transformer fed direct from a 3-phase breaker, when testing IR can i test it from breaker or do i have to disconnect from transformer? would the 500v damage the transformer?
2. was testing Zs at a start stop 3-phase isolator, it was only a 4-core cable so earth was obtained with the armour gland, when i was testing one of the phases to the lock ring there was a small arc and a small chard mark on the lock ring, is this normal, lock ring was solid and i got a good Zs for all phases?
3. when your looking to see how many points are on a circuit, is a double socket 1 or 2 points, is a spur and outlet 1 or 2 points, is a light switch a point, if a light has 4 bulbs is that 4 points?
1, Yes test from MCB, and No shouldnt damage Transformer, but a little vauge on the infomation.
2, It will arc if you dont hold the conection tight. I blew a hole through a kitchen sink when I was an apprentice! so dont panic.
3, Thats open for interpritation. I take its current using items. So a light is 1 a switch doesnt count. a sw spur controlling a socket is 1, a cooker pannel with socket is 2. (one for cooker one for socket) a twin socket is counted as one.
Reply to couple of questions in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
When he bought the bank, they stripped out all the metalwork, iron bars etc for scrap. He was left with the cashier countertops… which have been...
Haha yes, it is. Must be a northern expression. Have a Google 😂