This was installed by an "electrician" 4 months ago.Single RCD feeding 5 breakers for a two bedroom,two story house.
The lady was charged ÂŁ675 for this crap and was told she'd get a certificate,which no matter how much she rings them up,doesn't seem to be forth coming.I wonder why?
It really makes my blood boil when I see stuff like this and they even get away with charging over the odds for it.
 
That’s absolutely criminal....

who in their right mind starts with the lowest breaker next to the main switch
years ago, it used to be the norm to put the highest rated MCB next to the main switch and scale down along the busbar. it was as pointless then as it is now. my preference is not to put heavily loaded MCBs adjacent to each other, irrespective of rating.this is so you don't end up with 2 warm breakers warning each other.
 
What's at the other end of the tails?

Maybe it doesn't look too bad but BG is correct....she's been fobbed off.
Who knows the state of the installation as a whole? Whoever the installer, they should know the dangers involved and do the necessary before starting.
 
But if your a fully qualified 18th edition electrician then you should know that putting a single RCD on a house is a no-no.The lady said that he didn't do any testing around the house,took no readings and obviously no certs.It makes me wonder if this was done by a 3 week wonder?
Mate on here a lot of sparks argue with me for reasons not to have an RCD let alone 2. I always state a dual rcd split load consumer all the way and trying to comply with recommended board schedule layout yet most are happy with semi enclosed 3036. Good on you for pointing out this poor install.
 
Mate on here a lot of sparks argue with me for reasons not to have an RCD let alone 2. I always state a dual rcd split load consumer all the way and trying to comply with recommended board schedule layout yet most are happy with semi enclosed 3036. Good on you for pointing out this poor install.

Surely comparing BS3036 re-wireable fuses with a single upfront 30mA RCD is akin to comparing apples with tennis balls?
 
Surely comparing BS3036 re-wireable fuses with a single upfront 30mA RCD is akin to comparing apples with tennis balls?
Yes that’s been my point for months, years ?
[automerge]1597268848[/automerge]
Yes that’s been my point for months, years ?
My point has always been to upgrade and the fact that this particular post has an rcd is a relief to me. Although still not up to my standards it’s nice to see it’s covered with rcd
 
Yes that’s been my point for months, years ?

The difference being that, aside from lacking RCD protection, that old installation may be perfectly fine and will have met the regulations in place at time of installation.

The issue highlighted by the OP is a new installation that doesn't comply with current regulations.
 
My point has always been to upgrade and the fact that this particular post has an rcd is a relief to me. Although still not up to my standards it’s nice to see it’s covered with rcd

You state a preference for dual RCD boards which obviously meet current regulations (other than TT systems I believe), but why not recommend RCBO boards given that they are now available for little additional cost? Less chance of nuisance tripping for the customer and simpler fault finding, should problems occur in the future.
 
The difference being that, aside from lacking RCD protection, that old installation may be perfectly fine and will have met the regulations in place at time of installation.

The issue highlighted by the OP is a new installation that doesn't comply with current regulations.
Ahh no don’t fall into that trap as all the older more experienced electricians always mention about deviations from BS7671 yes at time of the install 40 years ago!!! It was fine. You test to the current regulations and times have changed unfortunately and our standards have improved. Dont lick arse on here to impress ppl
[automerge]1597269539[/automerge]
You state a preference for dual RCD boards which obviously meet current regulations (other than TT systems I believe), but why not recommend RCBO boards given that they are now available for little additional cost? Less chance of nuisance tripping for the customer and simpler fault finding, should problems occur in the future.
RCBO’s ??? you’re winding me up here surely do you know how much they cost?
 
Ahh no don’t fall into that trap as all the older more experienced electricians always mention about deviations from BS7671 yes at time of the install 40 years ago!!! It was fine. You test to the current regulations and times have changed unfortunately and our standards have improved. Dont lick arse on here to impress ppl

I'm not licking anyone's arse and I'm more than happy to stand corrected on any issue.

If you were testing the installation pictured in the first post, would it not be deemed unsatisfactory as it doesn't meet the regulations in place at the time of installation - ie the current regulations.

It's all very well having strong opinions about old installations, but it's a bit odd to defend a non-compliant new installation in the process of doing so.
 
RCBO’s ??? you’re winding me up here surely do you know how much they cost?

About ÂŁ12 nett for Fusebox Type A RCBOs.
[automerge]1597270275[/automerge]
Depends on the situation and reason for comparison, but it's not particularly unusual to find such a CU fed via a 30mA ELCB or RCD.

Indeed.

That reminds me of yet another cowboy electrician that worked on my parent's house. Many, many years ago someone explained to them why it was necessary to fit an ELCB, so they gave them the go ahead to do so. The ELCB was duly mounted by their meter, but never connected to the supply - sat there for decades with cable knockouts intact, while they assumed everything was much safer than before.
 
Last edited by a moderator:
I'm not licking anyone's arse and I'm more than happy to stand corrected on any issue.

If you were testing the installation pictured in the first post, would it not be deemed unsatisfactory as it doesn't meet the regulations in place at the time of installation - ie the current regulations.

It's all very well having strong opinions about old installations, but it's a bit odd to defend a non-compliant new installation in the process of doing so.
I didn’t say it was non compliant I said it was nice to see an rcd let alone 2 of them which I would prefer. This isn’t non compliant on the way I’m saying Rcd protection for lights and sockets for potential outdoor use. The other points then yes it’s not great but I’m stating I’m happy to see an rcd. Mate you seem like your fairly new to electrics don’t look for reasons to not upgrade look for reasons to improve safety
[automerge]1597270677[/automerge]
About ÂŁ12 nett for Fusebox Type A RCBOs.
[automerge]1597270275[/automerge]


Indeed.

That reminds me of yet another cowboy electrician that worked on my parent's house. Many, many years ago someone explained to them why it was necessary to fit an ELCB, so they gave them the go ahead to do so. The ELCB was duly mounted by their meter, but never connected to the supply - sat there for decades with cable knockouts intact, while they assumed everything was much safer than before.
About ÂŁ12 nett for Fusebox Type A RCBOs.
[automerge]1597270275[/automerge]


Indeed.

That reminds me of yet another cowboy electrician that worked on my parent's house. Many, many years ago someone explained to them why it was necessary to fit an ELCB, so they gave them the go ahead to do so. The ELCB was duly mounted by their meter, but never connected to the supply - sat there for decades with cable knockouts intact, while they assumed everything was much safer than before.
ÂŁ12 nett rcbos? Wtf are they mate ? most common rcbos are ÂŁ30 a pop Minimal and if you were doing a consumer unit upgrade you wudn be buying rcbos
[automerge]1597272035[/automerge]
What has that got to do with anything?
Think it has sumin to do with discrimination, I would never put the lowest sized breaker next to rcd just common practice to go down in size is that what you do?
 
Last edited:

Reply to Cowboy electrician in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top