This was installed by an "electrician" 4 months ago.Single RCD feeding 5 breakers for a two bedroom,two story house.
The lady was charged ÂŁ675 for this crap and was told she'd get a certificate,which no matter how much she rings them up,doesn't seem to be forth coming.I wonder why?
It really makes my blood boil when I see stuff like this and they even get away with charging over the odds for it.
 
I did an EICR for a 30+ Yr old install. 4 circuits and an RCD covering all.
I didnt fail it on this and didnt think anything of it....should I have???
IMO the circumstances of the installation would dictate the code. If the board was in a property with stairs and the occupier was elderly or infirm i would consider a code 2 appropriate. Regardless, if that was not the case and I coded it 3 then there would be a carefully worded recommendation that consideration should be given to the risk of a total power failure in the event of a single fault.
It must also be taken into account though that total power failures occur regardless of fault protection on the consumers installation.
 
Think it has sumin to do with discrimination, I would never put the lowest sized breaker next to rcd just common practice to go down in size is that what you do?
I cannot see any reason for putting them in a specific order - these days.
AIUI, with some of the older fuse boards, some of them had a single high current space next to the main switch which could take a higher rated fuse than the rest of the ways. So I guess this created a "rule" that the high power loads go next to the main switch, and this "rule" had been passed down from tradesmen to apprentices ever since - with no-one really thinking about the "why ?" :rolleyes:
There is an argument for spacing "heavily loaded" devices. MCBs or RCBOs that are loaded will heat up, and the heat will affect (reduce) the tripping current of adjacent devices. Putting a number of such loaded devices all together (very slightly) increases the risk of nuisance tripping.
ÂŁ12 nett of VAT - perhaps I should have been clearer on that point. There have now been two options posted in this thread for RCBOs well under your price of ÂŁ30 - CP Fusebox and BG - both of which are roughly half of that.
I'll add that SBS Trade Sales charge ÂŁ16 net for compact RCBOs (single module, 2 pole switching) - type AC or A, curve B or C.
i don’t agree with that from what I gather we are having dual rcd consumers as recommended for paat few years
There's a difference between "recommended" and "most cost effective way to meet regs". In practical terms, for most installations you need 2 RCDs minimum to meet specs - and back when dual-RCD boards came in, RCBOs were either non-existence (for some makes/models) or just stupidly expensive. So that really only left the dual-RCD board as an option.
As above, that is no longer the case - and a full RCBO board can cost less now than a dual-RCD board would have cost a few years ago.
NO, you do the fault finding there and then I would never leave a customer with 4 or 5 circuits without power untill next day. Why would you do that???
OK, you're on another job (or on holiday), the other side of the country, and a customer phones up because "half the house" has gone off. They can't reset one of the RCDs even with all the MCBs off - so please explain how you will fault find "there and then" and leave the customer with everything but the faulty circuit working ?
CP Fusebox compact RCBOs are finally available. Their size is of little relevance, but it's worth noting that they also disconnect neutral and bring another DP option to a market that will benefit greatly from competition on price.
Yes, some of the RCBOs have 2 pole switching - as do the SBS ones which are also just under ÂŁ20 inc VAT. You need to be careful exactly what's on offer - AIUI few of the single module devices have 2 pole sensing for the over-current, so they will switch the neutral, but not trip on neutral current (which shouldn't be a problem for most installs).


If you take that argument far enough then each individual socket, light etc would be on it's own RCBO protected circuit.
No, that would be reductio ad absurdum. But to a point, yes you are correct - it's why we don't (generally) put all the lights on one circuit, all the sockets on one circuit, etc.
A while ago I went to look at a fault in one of our lass's cottage - all the lights had tripped and she couldn't get them back on. There's an argument that at the time it was last re-wired, having all the lights (all 6 of them) on one fuse was acceptable. At some point, the bathroom (in a flat roofed extension) had been converted to a wet room, and as part of that they'd added an RCD to the lights. The fault was easy enough to guess - damp in an outside light.
These days I'd expect to see at least 2 light circuits in all but the smallest of properties - that's just one of those things where standard practices change over time.
 
Yes, some of the RCBOs have 2 pole switching - as do the SBS ones which are also just under ÂŁ20 inc VAT. You need to be careful exactly what's on offer - AIUI few of the single module devices have 2 pole sensing for the over-current, so they will switch the neutral, but not trip on neutral current (which shouldn't be a problem for most installs).

It wont be an issue for me as I've no reason to buy any, but interesting to learn this and it's something I'll have to read a bit more about.

I'd mentioned their new range of RCBOs after noticing they had finally been released and it seemed appropriate to mention in this thread.

No, that would be reductio ad absurdum. But to a point, yes you are correct - it's why we don't (generally) put all the lights on one circuit, all the sockets on one circuit, etc.
A while ago I went to look at a fault in one of our lass's cottage - all the lights had tripped and she couldn't get them back on. There's an argument that at the time it was last re-wired, having all the lights (all 6 of them) on one fuse was acceptable. At some point, the bathroom (in a flat roofed extension) had been converted to a wet room, and as part of that they'd added an RCD to the lights. The fault was easy enough to guess - damp in an outside light.
These days I'd expect to see at least 2 light circuits in all but the smallest of properties - that's just one of those things where standard practices change over time.

I took that reasoning to unnecessary lengths a couple of years back in my parent's home, by replacing 2 lighting circuits with 5. I'd decided to give the kitchen/utility lights their own circuit as it was fairly practical to do so and also liked the idea of them still having some downstairs lights on the off chance a fault should take out one of the circuits. Later when thinking about the outside lights, I figured potential water ingress was the most likely situation that might take out a lighting circuit, so figured outside lights could have their own way on the board - due to the distance between the front and rear lights, that 1 circuit became 2.

It was overkill, but there was plenty of space to do so and the additional cost wasn't particularly significant. They're old, they're my parents and they couldn't get anyone to fix a fairly significant fault, so when I found myself doing a job I'd rather not be doing, it seemed like a good idea to depart a little from convention and try to make things better for them.
 
I cannot see any reason for putting them in a specific order - these days.
AIUI, with some of the older fuse boards, some of them had a single high current space next to the main switch which could take a higher rated fuse than the rest of the ways. So I guess this created a "rule" that the high power loads go next to the main switch, and this "rule" had been passed down from tradesmen to apprentices ever since - with no-one really thinking about the "why ?" :rolleyes:
There is an argument for spacing "heavily loaded" devices. MCBs or RCBOs that are loaded will heat up, and the heat will affect (reduce) the tripping current of adjacent devices. Putting a number of such loaded devices all together (very slightly) increases the risk of nuisance tripping.

I'll add that SBS Trade Sales charge ÂŁ16 net for compact RCBOs (single module, 2 pole switching) - type AC or A, curve B or C.

There's a difference between "recommended" and "most cost effective way to meet regs". In practical terms, for most installations you need 2 RCDs minimum to meet specs - and back when dual-RCD boards came in, RCBOs were either non-existence (for some makes/models) or just stupidly expensive. So that really only left the dual-RCD board as an option.
As above, that is no longer the case - and a full RCBO board can cost less now than a dual-RCD board would have cost a few years ago.

OK, you're on another job (or on holiday), the other side of the country, and a customer phones up because "half the house" has gone off. They can't reset one of the RCDs even with all the MCBs off - so please explain how you will fault find "there and then" and leave the customer with everything but the faulty circuit working ?

Yes, some of the RCBOs have 2 pole switching - as do the SBS ones which are also just under ÂŁ20 inc VAT. You need to be careful exactly what's on offer - AIUI few of the single module devices have 2 pole sensing for the over-current, so they will switch the neutral, but not trip on neutral current (which shouldn't be a problem for most installs).



No, that would be reductio ad absurdum. But to a point, yes you are correct - it's why we don't (generally) put all the lights on one circuit, all the sockets on one circuit, etc.
A while ago I went to look at a fault in one of our lass's cottage - all the lights had tripped and she couldn't get them back on. There's an argument that at the time it was last re-wired, having all the lights (all 6 of them) on one fuse was acceptable. At some point, the bathroom (in a flat roofed extension) had been converted to a wet room, and as part of that they'd added an RCD to the lights. The fault was easy enough to guess - damp in an outside light.
These days I'd expect to see at least 2 light circuits in all but the smallest of properties - that's just one of those things where standard practices change over time.
I would obviously have no chance if I was away but would call in favours from my fellow sparks. If it’s still tripping with all mcbs off usually means a neutral earth fault so you need to unplug everything which is standard practice but yes many ifs and buts just saying I would do my best To ensure all is back to normal whether it’s me or someone else to get power back on
 

Reply to Cowboy electrician in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top