Hi all.. I have recently purchased a cooker and thought straight swap surely as cooker switch was above counter and the connection unit was behind the oven. Upon opening the connection unit I noticed someone has wired it using 3 6mm cpc singles. I then opened the cooker switch and it was fed with the same. It seems they have extended the cooker circuit. After removing a considerate amount of tiles I found where it was extended. The flat is wired in old 16mm conduit and singles. But the end box where they done the connections is about 500mm above the gas hob. Any ideas how I could rectify this. Getting the old stop end box of could be a nightmare as would rewiring the whole circuit. If I get a suitable way of connecting new 6mm cable to this point will a blank plate over the gas hob do the job?
Thanks in advance. I'm not quite sure how to upload a picture
 
Sensibly you should extend the conduit run to the correct point using an imperial to metric adaptor.
Alternatively you can run the continuing circuit in standard 6mm² H07RNF flex or twin and earth so long as you can also continue the earthing if this is provided by the conduit.
If the connection box has been there for a long time without problems then it should continue to do so, however it is not ideal and if you have the chance to change this then take it.
 

Reply to cowboy oven wiring!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
705

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
776
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top