when doing a p.i.r. on a commercial building(have only ever done them on domest) how do u measure r1+r2 or r2 on high level lighting cct ie unable to reach ??
Do u measure at the switch and put this in the limitations as this is the only point of possible contact under normal cicumstances ??
 
You are not likely in most of these sort of circumstances to be able to get a true R2 reading via the above method without disconnecting the CPC from the fitting,due to it being bolted to steel trunking,structural steel etc, you could get a low continuity reading even if no cpc was present. If the above method was used that should be noted on the cert.
 
PVC conduit ??

On a PIR I would have no problem with using method 2 for CPC continuity. If you had a factory with Hi bay or even banks of flourescents you wouldn't dismantle them to disconnect the CPC to test for continuity I'd use wander lead and method 2. After all your just prooving continiuty through the circuit

A PIR is not an intrusive inspection don't have my GN 3 with me but I think it even says that you can do more harm to the installation by over dismantling. If there were no previous PIR's or EIC and the installation was old or the eniviroment was particularly harsh then you may have to go down the road of major dismantling to get R1 + R2 to find the Zs for a circuit.

I honestly can't see a problem on the majority of PIR's with using wander leads and telescopic arms like these. Bottom line is there are no set tests as such for a PIR it's the inspectors call. In table 3.3 of the GN 3
Dosen't it also say that for CPC continuity can be achieve between earth terminal of distribution boards and the following exposed conductive parts..

Accesible exposed conductive parts of current using equipment.

I also think that there is a note recommending that accessibilty is just 3m standing.

As I said I don't have the GN 3 with me so maybe totally wrong, If I'am then sorry.
 
Didnt mean to trash your method malcolm,sorry if it appeared that way,I've done an R2 using similar methods before and you are proving an earth fault path is there.....But as stated you could concievably get a satisfactory reading even if no cpc was present at the luminaire,I would record the limitations of the method on the cert to cover myself,that is the only point I was making.
 

Reply to cpc continuity on pir in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top