Hello All
This will be my first post for a bit of direction sincejoining the forum a while ago, and this issue has us a bit baffled. It is possible me and my mate have overlooked something really daft & obvious! Anyway here it is..
Yesterday we were doing a periodic on my mates flat which is part of a block. These flats were built in 1968 so are near 45 year old. The C.U has labels stating the property was brought up to date in 2009 and next inspection is 2019. The flat has obviously been brought in line with 17th edition as the C.U is a 10 way dual split RCD type, there are two codes of wiring present. I believe initially the flat had one ring and with the 17th in effect the kitchen has had a new ring with new colours.
After deciding to do a full comprehensive of all circuits we checked the C.U for sequence & order of circuits and all looked neat and in order. We started with the first side of the split board with shower, kitchen ring, & boiler which all revealed test values quite normal, however when we got to the 2nd side of the split the ring circuit revealed a CPC end to end of 0.08, Line - 0.3 & Neutral - 0.3, with significant varying results after cross connection of L-N & L-CPC at each socket.
How is it possible that a reading for the CPC, with a reduced CSA, can be significantly lower than the line or neutral loop?? Scratching our heads, further investigation we did, removing the socket outlet with the highest value obtained which was a massive 2 ohm`s. What we found was no CPC. We removed near half of the other sockets to see what was going on and none had a CPCs present which brings me to the question:
How is it possible to get a continuity reading between Line & CPC with use of an R2 Box when there isn’t any CPC provided or more again how the CPC end to end value can be so low!
The only reason I can think of for the continuity at the sockets between L-CPC is that metal conduit is run through the walls and onlyt he screws securing the switchgear is enabling continuity. As for the 0.08 end to end, well I’m hoping we can get some direction right here!
Although it may have a reasonable logical explanation,please be gentle!
Thanks Jay
This will be my first post for a bit of direction sincejoining the forum a while ago, and this issue has us a bit baffled. It is possible me and my mate have overlooked something really daft & obvious! Anyway here it is..
Yesterday we were doing a periodic on my mates flat which is part of a block. These flats were built in 1968 so are near 45 year old. The C.U has labels stating the property was brought up to date in 2009 and next inspection is 2019. The flat has obviously been brought in line with 17th edition as the C.U is a 10 way dual split RCD type, there are two codes of wiring present. I believe initially the flat had one ring and with the 17th in effect the kitchen has had a new ring with new colours.
After deciding to do a full comprehensive of all circuits we checked the C.U for sequence & order of circuits and all looked neat and in order. We started with the first side of the split board with shower, kitchen ring, & boiler which all revealed test values quite normal, however when we got to the 2nd side of the split the ring circuit revealed a CPC end to end of 0.08, Line - 0.3 & Neutral - 0.3, with significant varying results after cross connection of L-N & L-CPC at each socket.
How is it possible that a reading for the CPC, with a reduced CSA, can be significantly lower than the line or neutral loop?? Scratching our heads, further investigation we did, removing the socket outlet with the highest value obtained which was a massive 2 ohm`s. What we found was no CPC. We removed near half of the other sockets to see what was going on and none had a CPCs present which brings me to the question:
How is it possible to get a continuity reading between Line & CPC with use of an R2 Box when there isn’t any CPC provided or more again how the CPC end to end value can be so low!
The only reason I can think of for the continuity at the sockets between L-CPC is that metal conduit is run through the walls and onlyt he screws securing the switchgear is enabling continuity. As for the 0.08 end to end, well I’m hoping we can get some direction right here!
Although it may have a reasonable logical explanation,please be gentle!
Thanks Jay