Is the main reason for having proportional sized cpcs for cables to ensure incase of fault they dont over heat and burn. Say using a 1mm earth for a 25mm sub main in a hyperthetical fault would overheat very quickly? Also "hyperthetically" if you were to use the earth in the neutral terminal say in a standard pendant with lamp and switched it on, would it work? Seeing as neutrals and earths are basically at the same potential and even the same conductor in PME systems. Im sorry for odd questions. I really love to overthink scenarios and what ifs.
 
i think OP was more concerned about selecting cpc's of sufficient csa to withstand a PEFC without damage. as you rightly point out, spin, sometimes less csa than live conductors simply to save money.
 
CPCs are required to carry high fault currents for very short durations.
Hopefully, they will never have to do the task they are designed for.
Live conductors on the other hand have to be able to carry low to medium amperage currents for long durations, as well as being able to withstand high fault currents for short durations.
In general, the higher the current, the larger the conductor.
However because the speed of operation of the Circuit Protective Device increases as the current increases.
With CPCs the opposite applies. The higher the 'fault' current, the smaller the conductor.
As such, as long as the impedance of the fault path is low enough to allow the CPD to operate within the specified times, in order to save money, the smallest size of CPC is used.
 
Last edited by a moderator:
CPCs are required to carry high fault currents for very short durations.
Hopefully, they will never have to do the task they are designed for.
Live conductors on the other hand have to be able to carry low to medium amperage currents for long durations, as well as being able to withstand high fault currents for short durations.
In general, the higher the current, the larger the conductor.
However because the speed of operation of the Circuit Protective Device increases as the current increases.
With CPCs the opposite applies. The higher the 'fault' current, the smaller the conductor.
As such, as long as the impedance of the fault path is low enough to allow the CPD to operate within the specified times, in order to save money, the smallest size of CPC is used.

Thanks everyone. Clears everything up!
 

Reply to Cpc sizes in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top