Table 54.7 states that cables 16mm or smaller shall have the same size line and cpc.
So why does T&E have a reduced size cpc?
So why does T&E have a reduced size cpc?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss cpc sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The reduced CSA of the CPC should be confirmed as adequate by the adiabatic equation.
So that would mean whenever T&E is used the adiabatic should be applied to each length of cable.
I'm sure there must be another reason, perhaps lost in the sands of time.
OK. 543.1.1., csa shall be (i) calculated in accordance with 543.1.3 OR (ii)selected in accordance with 543.1.4Don't think so, heres what it says.
"543.1.1 The csa of every protective conductor, other than a protective bonding conductor, shall be
(i) calculated ........543.1.3 (adiabatic)
(ii) selected ..........543.1.4 (table 54.7)
Very strange.
OK. 543.1.1., csa shall be (i) calculated in accordance with 543.1.3 OR (ii)selected in accordance with 543.1.4
i understand this to mean that it can be calculated with the adiabatic, or use table 54.7
From Guidance Note 5:
"Except for 1mm, twin & earth cables do not comply with Table 54.7 as the protective conductor is smaller than the live conductor. For circuits employing these cables, the adequacy of the protective conductor must be checked by using the adiabatic equation."