oxocube

Table 54.7 states that cables 16mm or smaller shall have the same size line and cpc.

So why does T&E have a reduced size cpc?
 
i think that is more for distribution cables as opposed to circuit cabling.
 
Don't think so, heres what it says.

"543.1.1 The csa of every protective conductor, other than a protective bonding conductor, shall be

(i) calculated ........543.1.3 (adiabatic)
or
(ii) selected ..........543.1.4 (table 54.7)

Very strange.

Edit - missed out 'or' as pointed out by telectrix
 
Last edited by a moderator:
The reduced CSA of the CPC should be confirmed as adequate by the adiabatic equation.

It's normally far more cost effective to calculate a CPC CSA this way-imagine what happens when you start increasing line & neutral CSA for volt drop and grouping factors-the CPC CSA will have to rise in proportion if selected from 54.7
 
So that would mean whenever T&E is used the adiabatic should be applied to each length of cable.

I'm sure there must be another reason, perhaps lost in the sands of time.

Oh the reason will be cost.

From Guidance Note 5:

"Except for 1mm, twin & earth cables do not comply with Table 54.7 as the protective conductor is smaller than the live conductor. For circuits employing these cables, the adequacy of the protective conductor must be checked by using the adiabatic equation."
 
Don't think so, heres what it says.

"543.1.1 The csa of every protective conductor, other than a protective bonding conductor, shall be

(i) calculated ........543.1.3 (adiabatic)
(ii) selected ..........543.1.4 (table 54.7)

Very strange.
OK. 543.1.1., csa shall be (i) calculated in accordance with 543.1.3 OR (ii)selected in accordance with 543.1.4

i understand this to mean that it can be calculated with the adiabatic, or use table 54.7
 
Last edited:
OK. 543.1.1., csa shall be (i) calculated in accordance with 543.1.3 OR (ii)selected in accordance with 543.1.4

i understand this to mean that it can be calculated with the adiabatic, or use table 54.7

That's right.
 
From Guidance Note 5:

"Except for 1mm, twin & earth cables do not comply with Table 54.7 as the protective conductor is smaller than the live conductor. For circuits employing these cables, the adequacy of the protective conductor must be checked by using the adiabatic equation."

I bet there ain't many sparks that know that, or have ever done that or ever will do that.
 
too right. you generally assume that it's adequate. however, the lower csa of the cpc in T/E will mean a higher resistance, thus a lower fault current, chicken and egg .
 
true. it's also designed to fit in that tight space between the line and neutral conductors in T/E cable. now that's the clever part, threading it through.
 
So how many cases do you know of where the adiabatic has been used to verify the cpc size in a length of T&E and it has come out as being inadequate? And what is the solution? Rip out your install and fit 4mm instead of 2.5mm then do the calculation again? Or run a length og G/Y single alongside the T&E?

How many people on here actually use the adiabatic on a day to day basis?
 

Reply to cpc sizing in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
493

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top