Hi people I can't open the sticky PDF file about using swa armor as cpc. Is there a calc? I'll give you a few details of the job.
25m length
6mm 2core swa (buried)
Fed from 60898, B40
Feeds garage db containing a 32a ring main and 6a lighting circuit all rcd protected. 3x dbl sockets and 6x50watt fluorescent lights.
Basically how do I work out that the armor is ok to use as cpc?
Thanks
 
Electricalserv I would usually do it that way if I was installing but it's already in under a new path. I'll check regs out tomoz as there in van as I've worked it out before just can't remember
 
Can't get any mathematical symbols to appear here. Anyhow, I believe it to be the equation in 542.1.3. Where it is not desired to calculate then refer to table 54.7.
 
sparks114, i believe you refer to 543.1.3, the adiabatic equation.
 
You need to provide a little more info, with regard to earthing system and Ze values if you have it?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Cpc
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Frosty69,
Last reply from
Sparky Ninja,
Replies
7
Views
1,048

Advert

Back
Top