Didn't say I agreed with it but it is a fact that the proposal to require the Regulation breached to be recorded against the Observation was rejected when the final draft of BS7671 was published.
Since when did you have to include the regulation number on the observation sheet?

Sorry wasn't meant as a direct reply to you
 
'Twas what I was taught on my 2391. Without the qualifier of the reg number the inspector leaves themselves open to the question of "who says" and (often) "you're making it up to create work for yourself "
 
I never quote Regs. on an EICR.
What I do is state the fault and quote the appropriate Reg. No.
For instance:
Lack of RCD protection for sockets intended for general use in accordance with Regulation 411.3.3.
 
I never quote Regs. on an EICR.
What I do is state the fault and quote the appropriate Reg. No.
For instance:
Lack of RCD protection for sockets intended for general use in accordance with Regulation 411.3.3.
So you do quote the reg number! Which is what I meant.
 

Reply to Crabtree c50 code 2 or not in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
488
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

Sockets will probably be ok on one, a little inconvenient in the event of a fault though, I'd probably like a 7th rcbo in. Wonder if hes linked...
Replies
93
Views
8K
suffolkspark
S
It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
830

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top