Hi all.

So the Crabtree old style in my hand failed the I delta n test (times 1). But passed the 5 times test.

So I have replaced it with the one in the board. Supposedly reconditioned - and that’s failing both tests but mechanical works.

I am wondering if I am missing something here with my testing.

I am testing through a socket outlet.

Anyone any ideas other than replace with new?
 
Have you checked for N-E faults? These can interfere with both MFT tests and the operation of the test button.
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
 
Thanks Wilco.

I certainly considered not swapping out the original - seeing as it passed the 5 times test - as as you say - is only for additional protection.

I’ve just swapped it out again - and it’s now working.

But - when I tested at the socket outlet - no joy - but tested at the board (to be honest) - and it’s fine.

I’d like to get my head round what’s gone on here.

Best get back to work.....
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
That handbook is out of date now.
 
So are you saying it is incorrect?
Yes.
531.3.6 RCDs for additional protection
The use of RCDs with a rated residual operating current not exceeding 30 mA is recognized as additional protection in compliance with Regulation 415.1. These RCDs shall be provided to comply with the requirements of Regulation 411.3.3.
RCDs for additional protection in AC installations shall comply with:
- BS EN 61008 series, or
- BS EN 61009 series, or
- BS EN 62423.
Where installed at the origin of a final circuit or a group of final circuits, an RCD with a rated residual current not exceeding 30 mA may provide fault protection and additional protection simultaneously.
NOTE: Consideration shall be given to the division of the installation (see Regulations 531.3.2 and 314.2).
 
Hi - yes, I read the BBB too. The regulation does not include the BS4293 devices, so my understanding of the regulation is they may not be used for additional protection. To this end Elecsa has stated -
"When the 17th Edition (BS 7671: 2008) was published, only BS EN 61008-1 and BS EN 61009-1 were still listed (Regulation 411.4.9 refers). However, this does not preclude the use of RCDs to BS 4293, BS 7288 and BS 7071, where appropriate, for fault protection and/or additional protection, provided they meet the relevant operating time requirements."
Just to confirm, are you saying this advice from Elecsa is incorrect? And so these devices may not be used?
 
That advice is both correct and incorrect.
Where such devices are installed in existing installations, then as the advice states, their use would not be precluded, provided they meet the relevant operating time requirements.
However their use would be precluded in a new installation or as a replacement in an existing installation.
In such circumstances, the designer/installer would have to declare it as a departure and attest that safety has not been compromised.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Crabtree RCCB not tripping -help!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
Wilko,
Replies
30
Views
5,682

Advert

Back
Top