From what i can gather of what Malcolm was describing, is a IT grounding system which is split similarly to a medical room set up, where you have what is known as a PA earth and PE earth system, both being isolated from each other. Although this arrangement is a form of clean earth, it's probably not viable for your small requirements, as it relies on an IT transformer fed via a mains/generator/UPS supply.
What your looking for, is a straight forward clean earth, which is completely separate from the Building/MET earth, and the easiest way to achieve that, is by the use of earth electrodes that are not under/in the influence of any other earthing arrangement. Your probably going to need RCD protection on top, as it's doubtful your going to get decent enough values to trip a breaker. Not unless the soil/sand is full of sulfates and chlorides etc...lol!!
So your initial thoughts were correct...