R

Richard3009

To obtain the readings R1+RN/4 and R1+R2/4
at each socket outlet, when the crossover connections have been made at the CU.

If using a modern all in one tester like an MFT1552, is this test swift using a 3 pin plug or are you having to use probes to select the particular pins at every socket.
 
As far as I'm aware with the Megger, all you'll be able to test is the line-earth (R1+R2) reading, as these are connections available for live tests on the 3 pin socket. I know there is some sort of neutral connection in there, but not sure whether you'll be able to test continuity. If you want to go by the plug in method, you can actually get Socket and See plug tops that have the required connections so you can just plug your 3 lead set into them.

One thing I have found when testing using the normal plug lead with the Megger, is that on some sockets one side has a significantly higher reading when on the 200mA test, which may throw a new person off if they're expecting all the sockets to be around the same value. It certainly confused me for a bit!!

The link to the plug top I was talking about is here: -

Socket and See SS130 SS130. Buy online or call
 
Last edited:
To obtain the readings R1+RN/4 and R1+R2/4
at each socket outlet, when the crossover connections have been made at the CU.

If using a modern all in one tester like an MFT1552, is this test swift using a 3 pin plug or are you having to use probes to select the particular pins at every socket.

Whats wrong with just making up a plug top with flying leads and connectors i use this method works a treat cheers spike
 
To obtain the readings R1+RN/4 and R1+R2/4
at each socket outlet, when the crossover connections have been made at the CU.

If using a modern all in one tester like an MFT1552, is this test swift using a 3 pin plug or are you having to use probes to select the particular pins at every socket.

Hi i did a ring final circuit continuity steps from the fuse board end to end line conductor got reading neutral to neutral reading OL the meter i am using is a kewtech kt61

Thanks

Mark
 

Reply to Crossover continuity ring main test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853
You could try this https://www.deskshare.com/ip-camera-viewer.aspx Ive got one similar to this but i think only ever used it a few times...
Replies
5
Views
869

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top