Hi Guys,
Just looking for some advice. I'm currently installing power to a workshop via a 16mm swa 3 core cable.
The question is, what size protective conductor should i use for the swa at the supply end. The length of
the run is approx 40 metres. Cheers,
 
I just thought i'd add that i'm aware the regs state minimum of 2.5mm if protected against mechanical damage and corrosion
but wondered if it's best practice to use larger cable, thanks again.
 
If your asking what size CPC to run with the SWA cable, the answer is you don't need one as the SWA is more than capable of providing your CPC needs. And that's whether it's a 2/ 3/ or 4 core cable.

If it's a PME supply single phase, you can use a 3 core, and use the 3rd core as your bonding conductor and the SWA as your CPC. However, if PME 3 phase you'll need to run that separate bonding conductor!! Keep the size the same as the core conductors, though you may probably get away with a 10mm conductor!!
 
Hi, yes it's a single phase and the 3rd core will act as the earthing conductor for the workshop final circuits. I'm just looking at the swa
itself, obviously this will need earthing at the supply end as per regs, just a bit unsure as to what size cable to use for this. By the way, it's a TNS supply.
 
Hi, yes it's a single phase and the 3rd core will act as the earthing conductor for the workshop final circuits. I'm just looking at the swa
itself, obviously this will need earthing at the supply end as per regs, just a bit unsure as to what size cable to use for this. By the way, it's a TNS supply.

If TN-S then the SWA really needs fly leads at both ends not just at the supply end!! The 3rd core being connected directly/indirectly to the workshops EMT... 6 to 10mm fly-leads will suffice for a 16mm cable, or as suggested use the Adiabatic Equation... lol!!
 
Thanks for that, i was intending to use the fly leads at both ends anyway but was going to use 16mm. I'll probably go with eng54's suggestion and use 10mm, thanks again for the advice, much appreciated.
 

Reply to csa of protective conductor for swa cable in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top