mornin 2 all,got a problem with a square d power logic 750 meter controller,Brown phase not being registered on the amperage scale,other phases r ok.Now the easier way ou of this get square d bac & check it out,but those in ctrl dont want that easy option.We hav drwaings offa square d,but these do not tally up wiv the way its been wired,basically is it ok 2 have the S2 connection on the cts wired 2 the +,on there drawing they r wired 2 the _ which is the commoned to all other cts,any ideas ta ra bab cheers
 
Any chance of that in English?
Ok ,the cts registerin the current to the controller,r connected differently from their supplied drawing,the brown phase is not registerin the curent,does any1 think that the S2 connection on the ct is usually wired to the positive,on their drawing they shud b wired to the negative,is this relevant 2 why the brown phase is not registerin the current,S1 & S2 r the ct connections,hope thats a bit better cheers ta ra bab
 
You need to test the output from each CT. But for god’s sake open circuit them while they under load, either you or the CT will be fried. You are best to use an analogue meter.
Why don’t your company want to get the makers back?
 
Well after using the enigma machine on your post ...............I can only say are all the phases wired up the same as the brown phase? If they are are they working ?

If you answer yes to this then check that you don't have either a duff coil or meter.
thanks tony,all phases r wired up the same,looks like a duff ct,cheers
 
You need to test the output from each CT. But for god’s sake open circuit them while they under load, either you or the CT will be fried. You are best to use an analogue meter.
Why don’t your company want to get the makers back?
Its a long story,its a job we took over from a bust firm,the panel been standing around 4 ages,electrics jus recently been energised,& so this problem came up,Square D,wants a fortune 2 jus look at it cheers 4 your help ta ra bab
 

Reply to Ct not registerin current in the Electrician Talk | All Countries area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks